Hi people, just wondering the best way to install these 12v transformers, are there any regs requiring a fire hood or cover over them as I can imagine they get warm? I've installed fire rated down lights which sit in the loft space and was worrying about the insulation near the transformers I will leave space around just thinking if someone decides to cover again! Thanks
 
At Murdoch says, fit 240V downlights.

I mostly refuse to install 12V ones nowdays, but explain instead how it would be much better to have LED lamps running at e.g. 5W (instead of 50W), and I either install GU10 LED ones, or sometimes integrated LED assemblies. You eliminate most of the heat, and the lamp holders that sometimes fail, plus the transformers that also sometimes fail.
 
if insulation is chucked in, the transformers will be the least of his worries when the halogen loft heaters cause a fire.
 
thanks for the replies , its in a bathroom they are ip65 know they could be 230v just being extra safe, ill look into leds for next time .
 
with the low price of 230V GU10 LEDs now being under a fiver, it's a no brainer.
 
I stopped the 12v 10yrs ago, technology has replaced them and all the problems that came with the tx kits and lamp burnouts due to spring grips relaxing on the pins over time.

I refuse to fit them now...GU10 with several lamp options to fit are the all rounder at the moment.
 
Okay am I right that if the fittings are IP65 then 230v fittings can be used in bathrooms and kitchens? and a reg number to back this up? thanks
 
if in zone 1, they need to be IP44 or better. check ceiling height. if above 2.25m, its outside zones correct me if that height is wrong. i can't get to grips with these foreign sillymeters)
 
As its a bathroom even if they fall height wise out of zone you still have to consider the environmental effects so I would still be fitting 'shower proof fittings' as they are known over baths and shower and if a heavily tiled bathroom, with little or no ventilation then I would fit throughout as they tend to get steamy easily and condensate to surfaces.
 
Nope, OP is on about filling out MWC in another thread! He's a trainee, perhaps he should post there
 