From my research it seems many Sunny Boy inverters are transformerless which means that there is usually no galvanic isolation between the PV dc input and ac output. If you tell me the model number of the inverter I will delve further.

I thought of an experiment you could do which might determine whether the leakage current waveform is ac or dc. At the moment the RCD is type B which can detect the waveforms ac 50Hz, ac 50Hz pulsed, Smooth dc, and ac greater than 50Hz into kHz region - see page 7/21 of:

http://www.doepke.co.uk/download/Techpub-16

The type AC RCD commonly used in Consumer Units can only detect ac 50Hz - it is blind to ac 50Hz pulsed, Smooth dc, and ac greater than 50Hz into kHz region.

What you could try then is inserting a type AC 30mA RCD upstream of the current type B and then observing what happens every morning to the type AC one -does it or does it not trip?

Just an idea for your consideration which might cast a bit more light on the problem by giving information on the waveform of the leakage current (as well as my # 15).
 
Re #24: What you could try then is inserting a type AC 30mA RCD upstream of the current type B and then observing what happens every morning to the type AC one -does it or does it not trip?

I am not suggesting removing the Type B.
 
Answer yourself - I will be interested to read your reasoning.

I have provided a reference which explains why it is right an RCD type B is intalled because there is no dc - ac side galvanic isolation. It may well be the manufacturer of the in-use Sunny Boy inverter says one is not required - one for the OP to clarify - though for me the presence of the type B RCD indicates that the installer has read and abided by the manufacturer's instructions.
 
Answer yourself - I will be interested to read your reasoning.

I have provided a reference which explains why it is right an RCD type B is intalled because there is no dc - ac side galvanic isolation. It may well be the manufacturer of the in-use Sunny Boy inverter says one is not required - one for the OP to clarify - though for me the presence of the type B RCD indicates that the installer has read and abided by the manufacturer's instructions.
The reference you have provided indicates that where required, B type RCDs should be used. i.e. circuits of locations containing baths or showers, socket-outlets or cables concealed in walls.
There is nothing there stating that the supply to or the output from the inverter requires RCD protection.
The OP says that the RCD protects the circuit to the inverter and that the circuit is wired in SWA.
 
At page 12/20 para (iv) of:

https://www.electricalsafetyfirst.org.uk/mediafile/100117576/Best-Practice-Guide-3.pdf

(iv) Where a microgenerator having a d.c. source does not incorporate the equivalent of a transformer providing at least simple separation between the d.c. and a.c. sides, an RCD installed for fault protection by automatic disconnection of supply or for additional protection (I∆n <_ 30 mA) must be of a type that will operate as intended in the presence of d.c. components in the residual current. (This does not apply where it has been established – such as from a specific written statement given by the inverter manufacturer – that the inverter provides galvanic isolation between the d.c. and a.c. sides that prevents it from feeding d.c. current into the electrical installation.) Note. A Type AC RCD will not fulfil the above requirement. Depending on the level and form of d.c. components, an RCD (where required) will need to be of Type A to BS EN 61008 or BS EN 61009, Type B to IEC 62423, or Type F to IEC 62423. However, in the case of a PV power supply installation, Regulation 712.411.3.2.1.2 of BS 7671 stipulates that the RCD (where required) shall be of Type B.
 
At page 12/20 para (iv) of:

https://www.electricalsafetyfirst.org.uk/mediafile/100117576/Best-Practice-Guide-3.pdf

(iv) Where a microgenerator having a d.c. source does not incorporate the equivalent of a transformer providing at least simple separation between the d.c. and a.c. sides, an RCD installed for fault protection by automatic disconnection of supply or for additional protection (I∆n <_ 30 mA) must be of a type that will operate as intended in the presence of d.c. components in the residual current. (This does not apply where it has been established – such as from a specific written statement given by the inverter manufacturer – that the inverter provides galvanic isolation between the d.c. and a.c. sides that prevents it from feeding d.c. current into the electrical installation.) Note. A Type AC RCD will not fulfil the above requirement. Depending on the level and form of d.c. components, an RCD (where required) will need to be of Type A to BS EN 61008 or BS EN 61009, Type B to IEC 62423, or Type F to IEC 62423. However, in the case of a PV power supply installation, Regulation 712.411.3.2.1.2 of BS 7671 stipulates that the RCD (where required) shall be of Type B.
Yep, as I said.
 
Please provide an argument with reasons using your knowledge of electrical engineering, the wiring regulations, awareness of the law for the safe use of electricity and appreciation of the installation in question.
 
Please provide an argument with reasons using your knowledge of electrical engineering, the wiring regulations, awareness of the law for the safe use of electricity and appreciation of the installation in question.
I’ve asked you why the RCD can’t be removed.
All you’ve done is provided a link to a source which states that any RCD in the installation will have to be a B type.
Something that I am well aware of.
You have not given any reason as to why it can’t be removed.
Now (though you’ve not answered my question), you want me to explain in depth why an RCD is not required.
The simple fact of the matter, is that from the information provided, the RCD is unnecessary, it’s not required as far as BS7671 is concerned and at the moment it is causing a nuisance.

Now your suggestion, is to install an incorrect RCD to see if that will or will not also trip.
So if it trips, what then?
If it doesn’t trip, what then?
Who pays for the installation of this unnecessary and incorrect RCD?
Most of these inverters have inbuilt RCD protection and they also show error codes if there’s a fault.
Having an external RCD, is probably preventing the inverter from logging any fault.
 
Last edited by a moderator:

Reply to Fitting a 100ma RCD on Solar PV to solve nuisance tripping. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
877
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock