Hi all,

Can anyone tell me where I in the reg's, if anywhere it states whether a multiplier of 1.8 should be used for calculating the design current of fluorescent lighting loads?
 
It doesnt...

The 1.8 figure is a rule of thumb for power factor on discharge lighting...

Get the actual ratings of the fittings for the design...
 
The 1.8 multiplier allows for when a number of capacitors within a circuit comprising of fluorescent luminaires eventually give up the ghost. Normally when a capacitor fails you would expect the power factor to drop to around 0.4 per fitting which essentially means that your bog standard 2x58W fitting shoots up to drawing an apparent power of around 300W instead of around 100W.

It is acceptable to design circuits comprising of fluorescent fittings without using a multiplier but unless you are either factoring in regular preventative maintenance of the installation or installing HF fittings or PFCUs then it would be prudent to use it.

A fundamental understanding of the science and principles of electrical installation would be able to tell you that your circuits should be designed to cope with the current being drawn. You don't need a regs book to tell you this.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fluorescent Lighting multiplier
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
Daibhid,
Last reply from
D Skelton,
Replies
4
Views
7,517

Advert

Back
Top