jase
ok as long as you are aware of the deviations and note them down, and then if they are picked up by the assesor you can answer any questions on them
You dont have to upgrade 6mm bonding with a C/U change, just put it as advisory. Thats what elecsa say anyway.
Not just ELECSA. It's on the ESC Forum which is agreed by all the schemes and the IET.
shed is spurred of a 13a fcu, swa is 4mm live conductors and 2.5mm cpc, buried cable. The junction box in the shed looks as if it would fail it's ip rating as i could easily stick a finger in there.
where is the 2.5 cpc in relation to the swa??
inside the sheath(line, neutral + cpc), just went out to shed to check, i think they are all 4mm stranded conductors.
even for PME??

I just read the Best Practice Guide for changing a consumer unit downloaded from the ESC website, and it does say on 6.1-6.3 that the earthing arrangements must be adequate before work is begun![]()
how did the assessment go tok??
how strange i thought i had replied!
The assessment went ok, the assessor said that the bonding had been "adequate", and i promised to finish upgrading it to current regs.
All the extensive testing i did was a bit wasted as he was more interested in the fundamentals and was happy with how the certificate looked, plus i had all the paperwork prepared.
I was ready to impress him with all my knowledge of circuit design, regs etc. , but he didn't really quiz me very much!