C

CraigL

Hi all,

New to the forum so thanks in advance for your help.

I've just fitted a garage board details below:
Main Consumer Unit is Dual RCD - whoever did the re-wire had already fitted 6mm t&e direct from cu into an external jb. I've connected the t&e to swa (house end) and at the garage end the swa is fitted direct to the garage board.

The garage board is a dual board with an rcd main switch. At present I have it connected with rcds on both sides, and it is working fine. Note the garage is only used for storage and rarely used, it's not being used for a workshop. Therefore imo there is no danger caused by having rcds at either end, merely an inconvenience due to any tripping- but I don't want to leave a job if there is a 'realistic' better/safer option.

My understanding of the best option for installing a sub-main in a garage is to have the garage board rcd protected and the feed from the cu from a non-rcd protected breaker - and therefore no inconveniece tripping. However the consumer unit is dual rcd, so how is possible to fit a non-rcd protected breaker?

It's been suggested that I could have changed one block to rcbos, except the garage board breaker - but then it's an additional expense. Alternatively is it possible or even allowed to remove one of the ways from the busbar, and therefore leaving a spareway not connected to any rcd and take a direct feed from the main switch to this breaker - but this would mean 3 lives leaving the main switch, which I don't think would fit? Or could I take a feed from the live side of one of the rcds. In doing this surely I would have to fit another neutral bar and therefore I would be changing the board from it's initial design, implications??

Thinking allowed as I'm typing, even if it is possible to achieve the above scenario, doesn't this mean that the t&e from the cu to the external jb is now non-rcd protected...

Thoughts??

Thanks
 
Michael, you have missed some essential points.

1. The new tails (heading towards the garage) MUST pass through a current limiting device. RCDs do not limit the current.
So a switch/fuse is needed at that point (I think I detailed this in this thread about 6 months ago. I CBA to read all the way back).
The fuse needs to be appropriate for the SWA.

2. A time delay RCD (or any RCD) is NOT necessary at the house end.
 
Michael, you have missed some essential points.

1. The new tails (heading towards the garage) MUST pass through a current limiting device. RCDs do not limit the current.
So a switch/fuse is needed at that point (I think I detailed this in this thread about 6 months ago. I CBA to read all the way back).
The fuse needs to be appropriate for the SWA.

2. A time delay RCD (or any RCD) is NOT necessary at the house end.

Absolutely agree about switch fuse, schoolboy error.

I agree time delay "might" not be necessary, but it gives another level of protection I think is worth the extra small cost.
 
Dave, unsurprisingly you are correct. Had time to check my understanding this morning. Obvious when you take time to think about it.

So best solution would be pull tails from house CU into service block. Then new tails into house CU and new RCD enclosure with time delay RCD. Then SWA to garage CU with RCD.
Cheap simples and best soloution. Any fault in garage will only trip garage RCD, with SWA cable also protected by time delay RCD.

Why the time delay RCD?
 
No, please do start as this thread has improved my knowledge which has got to be a good thing. And hopefully for others.

Agreed time delay RCD does not provide shock protection, but it does still provide earth leakage protection. So I'm still thinking it's a good thing ?
 
So that begs the question; what use does a time delayed RCD have?
We know it must be used for RCD's in series.

Time delayed RCDs are used to achieve discrimination where the upstream device is providing fault protection because the required EFLI for the mcb or fuse cannot be met. For example TT systems where you can rarely achieve a low enough Ra to allow mcbs or fuses to operate in the required time.
 
As a s type max allowed tripping time is 500ms and 130ms min tripping time then I wouldn't particularly use it where you need a disconnect time of 0.2 seconds for final circuits upto 32 amps(depending on rcd tripping time when tested) 100ma standard device would be used for fault protection only.
Where a s type is useful is protecting tails entering a metal enclosure and distribution/circuits above 32amps which have generally a 1 second disconnect time and discrimination against downstream rcds.
For a TT system
 

Reply to Garage Board - achieving discrimination? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock