rite...progress (at last)...now, any extranoius in that garage?
http://img442.imageshack.us/img442/5835/20130414155600.jpg shows the separate RCD.
So it looks like im ok to install a 30mA RCD in the garage.
OK pal.Cheers ipf, thats why i mentioned my industrial experience in the first post... Need a bit of guidance
In the picture it shows a 80amp rcd, some chunky sockets they must be!
True, but he's not installing the sockets. Easy to change for a 32amp, if he feels obliged
Edit: 32amp supply so OK
he is fitting a socket in the shed!
no....the supply cable will be protected by the 20A OPD in the house....The garage / shed sockets will be protected by 20a in the house cu and 16a in the garage cu.
so you know what your doing now?..Well yes the 20a in the house is there to protect the cable.
Thanks to everyone for clearing up the RCD questions.
TN-S you would treat the same....Yes im clear now thanks.
Back to motors and plc's tomorrow yipee!
For future reference, what if the system was a TT or TN-S?