Cheers ipf, thats why i mentioned my industrial experience in the first post... Need a bit of guidance
OK pal.
Correctly terminated (at both ends) 2.5 swa, no RCD req, with 20 amb c/b supply. Garage - con unit with 30ma RCD, 16 or 20 amp c/b for power, 6 amp for lights. Test and certify as req, job done. Good luck.
(as long as that tn-c-s system is all above board):icon14:
 
Glennsparks - the garage electrically is one light fitting and two double sockets. There are no structural steel-work or water / gas service parts in there.

worzol - house sockets protected by 32a breaker ;-)
 
The garage / shed sockets will be protected by 20a in the house cu and 16a in the garage cu.
no....the supply cable will be protected by the 20A OPD in the house....
your finals in the shed will be protected by the 16A OPD in the garage....together with additional protection (RCD)
 
Well yes the 20a in the house is there to protect the cable.

Thanks to everyone for clearing up the RCD questions.
 
Yes im clear now thanks.

Back to motors and plc's tomorrow yipee!

For future reference, what if the system was a TT or TN-S?
 