No offence to the OP I have been saying this for the past year on this forum that cryptic questions are no good especially guys who are trying to train up take critic badly but don't realise that we are trying to get them into a way of thinking that when they ask a question they supply as many facts as possible a bit like I will name that tune in 10 but don't expect me to do it in 2 lol
 
The simple answer is NO, you can't use the suppliers earth. To do so puts the utility personnel at risk. Simple enough for you?

Thank you very much for that, that's all I wanted to know you have been a great help
 
I realy can’t understand anyone undertaking a job they clearly have no knowledge of. They are not only a danger to themselves but more importantly to others.
If something goes wrong with generator earthing then it puts people in danger. If this was a planned power outage the DNO should advise on temporary feeds, it should not be the responsibility of the customer or appointed electrician.
On the MV courses I’ve been on it’s always pointed out the dangers from generator earthing and back feeds. It’s not a field for the average electrician to enter without the required knowledge.
From what the OP has said it would seem the job has been done. I find it amazing that someone would come after the event for safety information.
 