I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of power outages. The cable run from the generator to the outside mains incoming box will be about 40 meters. I intend to use 16mm SWA for that run. The generator control box has metering, fusing and an RCD. It's modern and made entirely by Mecc Alte. Not some Ebay Chinesium device.

Once the SWA is at the outside wall box where the underground feed from the supply company exits and the meter and master switch, 100 Amp utility company fuse is located, can I delete the two pole fused master isolation switch and use the two pole 125 Amp break before make change over switch and separate fuse as both an isolation switch to the house distribution panel and as a change over switch? I see a similar question was recently covered, but it was unclear as to whether doing this was advised against or regulated against.

Space inside the wall mounted outside box is limited. The alternative is to bring tails outside the box, to another water proof cabinet with the change over switch in, and return the cables back to the utility company box. Messy...

The property, a domestic bungalow, and has a PME earth system, how should the cabling from the generator be wired with regard to earthing at either end?

Thanks.
 
Can you post a picture of the meter box so we can be clear on what switchgear is currently installed in there?
 
Can you post a picture of the meter box so we can be clear on what switchgear is currently installed in there?
I should be able to do that tomorrow, but basically incoming SWA service cable from underground to 100 Amp service fuse, then meter, then to a two pole fused switch and onwards to the consumer unit within the house. There are a couple of junction boxes in there, too, where outputs FROM the CU in the house splice into SWA cables to outside lights and to the garage. Thanks for your reply.
 
Here's a photo of the inside of the supplier's wall cabinet, the fused switch to the consumer unit inside the house has an 80 Amp fuse in it. The other fused switch has a 63 Amp fuse in it and serves a dedicated panel in the garage for a 63A socket for my TIG welder.mains-box.jpg
 
Last edited by a moderator:
Looking at the wiring in that meter box I would suggest you employ an electrician as I doubt that the additions in that meter box have been ever been tested and parts do not appear to be compliant with the regulations

With a 2 pole changeover switch I would have concerns about the earthing still being connected to a PME system in the event of a power cut as it could be unreliable as an earth point and in the event of a fault could introduce fault currents into other properties located nearby
 
That looks rough, and there are boxes feeding various bits that kind of look like no over current protection, etc. As @UNG says you really should be getting that lot tested and documented before considering anything new.

As a first point of principle you should get an isolator switch that isolates everything, so all of the various things are down-stream of that including any transfer switch. It is the only safe and above-board means of working on the supply side of any CU to fit or fix the transfer switch, etc.

You must have an independent means of earthing any generator as you cannot assume the supply earth connection would be intact in the event of a fault that made you need to use the generator. A generator of that size would still be a TN supply (earth and neutral common at the generator) but that needs to be referenced to the true Earth by means of a rod or similar.
 
Althought the wall cabinet is owned and maintained by the property owner, the space inside is (supposed to be) reserved for the DNO and Energy supplier, apparently it's a condition of supply and is mentioned in their terms and conditions.

So if you are proposing altering any of what's there (excluding meter and fuse cutout) the simplest thing to do would be to move all the switch fuses to a new adjacent box and install the changeover switch in there.

If the meter needed to be changed to a "Smart Meter", either by request or the existing one going past it's use-by date or it failing, then I suspect the supplier would refuse to fit one as there would not be enough space.
 
OK, thanks for then replies, I imagine various things have been added on over the years and it has become somwhat of a pig's ear in there. What sort of secondary box would be required, are the regulations about that? I would like to have one mounted and ready for an electrician to populate, with any cable gland holes drilled to suit. Do cables between two boxes need to be SWA, or can T&E or tails in conduit be used? The SWA cable feed to the garage would really need to remain as it goes straight down into concrete and I will not be wanting to start digging up the concrete...
 
Cables in the boxes must have secondary insulation, so tails (double sheathed single conductor) or T&E are fine as it is not exposed to UV light or likely to be damaged by rodents, etc. You should take care that any holes have protection to avoid damaging cable going between them so grommet, gland, conduit, etc.

The SWA coming up to that adaptable box could be tidied up with a new box and cable exiting to the new adjacent meter-style box (assuming it can go to the right of current one). I would re-do the cable gland so it has the cover for the exposed armour in place, though maybe it is tight to assemble it given the stupidly short bit left out of the concrete!
 
Cables in the boxes must have secondary insulation, so tails (double sheathed single conductor) or T&E are fine as it is not exposed to UV light or likely to be damaged by rodents, etc. You should take care that any holes have protection to avoid damaging cable going between them so grommet, gland, conduit, etc.

The SWA coming up to that adaptable box could be tidied up with a new box and cable exiting to the new adjacent meter-style box (assuming it can go to the right of current one). I would re-do the cable gland so it has the cover for the exposed armour in place, though maybe it is tight to assemble it given the stupidly short bit left out of the concrete!
Thanks, that's very useful, will order a new secondary cabinet and call the sparky.
 
Resurrecting this as I have been away. The electrician rewired the outside supply box and added a second box with the two pole transfer switch in it. He wired a 125 Amp socket in the workshop tp plug the generator into. What I find is the generator makes power and although the house lights work, the consumer panel RCD trips. I think only the sockets are on the RCD as all the house LIGHTING circuits work OK on the generator.

The generator has neutral and earth bonded n the alternator box and it has the chassis grounded to a six foot earth spike near the machine. The outside electricity board box states the supply is a multiple earth system. What would cause a presumed earth loop that would trip the consumer panel RCD please? The electrician is away abroad on holiday. .... Thanks.
 
He wired a 125 Amp socket in the workshop tp plug the generator into.

That should be a plug (aka inlet connector) and not a socket which is installed for the generator to connect to. The socket must be on the generator side of the connection.
What I find is the generator makes power and although the house lights work, the consumer panel RCD trips. I think only the sockets are on the RCD as all the house LIGHTING circuits work OK on the generator.

Does the changeover switch isolate the whole installation or does any part of the installation remain connected to the grid supply when the generator is in use?
 
That should be a plug (aka inlet connector) and not a socket which is installed for the generator to connect to. The socket must be on the generator side of the connection.


Does the changeover switch isolate the whole installation or does any part of the installation remain connected to the grid supply when the generator is in use?
The changeover switch is a 2 pole break before make affair, So live and neutral are switched. Gennie ground is permanently wired to mains ground in he service provider box. Thanks for your interest.

BUT, I have now found this out:

OK, nailed it I think to the consumer unit in the garage. House consumer unit has a 32 Amp MCB that I was TOLD was for the garage, and is marked as "Garage". With that and ALL other MCB's off on the house CU as soon as i turned the main house consumer unit isolation switch on the main RCD tripped. If I turn the master switch on the garage consumer unit OFF all is OK. If the garage CU is turned on, even with all the MCB's OFF, the house CU RCD trips and it's a 100mA one.

I just need to get my head around how the housebuilder wired this stuff up, and why, with all MCB's OFF on both the house and garage CU's but the main CU switches ON, and the garage CU master switch on, it trips....

On normal mains these all work as expected.

Anyway the gennie runs EVERYTHING in the house and workshop, including a rotary three phase converter and all the workshop stuff without even getting to half its load capacity, which was the main purpose of the installation test :)


One MCB in the garage consumer unit didn't like the inrush to an air bottle compressor and has had repeated resets over the years, maybe that MCB is knackered but I can't think why it would cause a Live / Neutral imbalance which is what should trip an RCD, surely?

Things may be clearer tomorrow whilst I get to grips of it in my mind. <LOL>
 