Hopefully the N-E fault you have found is enough to explain things, though to trip a 100mA RCD you would need > 50mA and at 400 ohms that is 20V N-E which is really quite high for any sane cable voltage drop that you would plan (e.g. 5% is 11.5V and if L and N cables identical, then under 6V drop expected along N to appear N-E).
But it needs fixing anyway, so one done check and see if it has solved it.