nigbuzz

Hi,

I was called out to try and sort out flickering Halogen lamps in a lounge. There are a few GET digital dimmers which only control 1 20W LV downlight above pictures. Having spoken to there technical folks they said that the minimum load for these dimmers are 60W, so i replaced the lamp with a 50W and it worked a bit better but not for a great deal of time. I did some research and found that danlers do a reactive load which you can place in front of the transformers to fool the dimmer into thinking it has the right power on the circuit. Having spoken to Danlers about the problem they said they have never tired there reactive loads with other makes of dimmers, so my question is has anyone come across this problem, and would it work. as i don't want to break the dimmers if i put them in.

cheers
 
Danlers Resload is a power resistor mounted on a heatsink, selected to provide a 10W minimum load usually for dimmers controlling LED lamps. If you intend to use this as a solution to your problem you will require a least 4 Resloads (with a single 20W lamp) to compensate for the 60W minimum load of your dimmer, this is obviously inefficient and costly (£80+), plus there is the problem of where to put these loads so they can dissipate the heat safely. A cheaper and better solution would be to change the dimmer for one that requires a much lower minimum load, ideally <20W so that load resistors are not required. Or alternatively, you could try to persuade your customer to add two or more pictures and extend the existing circuit to include the extra lamps required.
 
Last edited by a moderator:

Reply to GET digital dimmer with Danlers RESLOAD will it work? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What is the oldest dimmer switch you have seen in use recently? When did you install your first dimmer? (Veteran sparks only) I ask because a...
Replies
18
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hey everyone I am looking at getting away from dealing with customers (haha) an am looking to get into site work. I have ECS Approved gold card...
Replies
0
Views
812
Three images are attached here. Two show the dimmer switch connections and one shows one of the two light fittings. There are two identical...
Replies
15
Views
3K
Hello! I am trying to install a smart fan/light dimmer combo switch (Treat life). I have installed one of these before in another location of the...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock