How many floors is the property? Around my way HMO's require manual call points. I've never had a drama with customers saying they didn't want them...you need a panel, emergency lighting etc so they don't really look out of place imo.
 
Not uncommon for the separate dwellings to have Part 6 detection also. Is the kitchen communal because that is high risk and should form part of the Grade A system. Don't forget to allow for a zone plan this is a requirement of BS5839:1
 
3 floors with the loft conversion bedroom. I agree with you bud, the landlord don't live there so she won't see it from here house.
 
  • Like
Reactions: Leesparkykent
Not uncommon for the separate dwellings to have Part 6 detection also. Is the kitchen communal because that is high risk and should form part of the Grade A system. Don't forget to allow for a zone plan this is a requirement of BS5839:1

Yeah communal kitchen is include that as part of the grade A on the panel system. Yeah I've got that on my to do. I maintained the fire alarm and sprinkler system at John Lewis distribution centre for 18 month, that was less hassle then this.
 
That councill letter is asking for interlinked smoke alarms why on earth are you installing a fire alarm???
 
There is different requirements if the property had 3 floors so can't get away with aico's etc.
 
since the Grenfell tower fire most land lords have to step up to the plate .
regarding the property you are working is HMO and fire panel is in order .having read
that letter from the council to you client .you need to read carefully.
e.g. fire doors .
 
That councill letter is asking for interlinked smoke alarms why on earth are you installing a fire alarm???
Because it asks for a Grade A LD2 system a hybrid of the Part 1 and 6 systems. High time this was restricted to Part 1 systems.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Grade A LD2 fire alarm advise
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
No1bacon,
Last reply from
No1bacon,
Replies
28
Views
13,099

Advert