hello all,

having a complete meltdown on a job this afternoon and i need an answer to what i think may be a very very stupid question.

if on an energised circuit you disconnect the neutral at the board (lighting circuit) will that removed neutral rise in voltage too to potentially 240v? reason i ask is I've been chasing what i thought was a live switching fault all afternoon and suddenly realised it may be a neutral issue somewhere?

thanks all,
gavin
 
i think it would as the "neutral" doesn't have a reference point to keep it at 0v, so would rise with the voltage of the rest of the circuit, but, as i said may just be having a brainfart.....
 
Depends if there's lamps (bulbs) in the fitting and whether the switch is on or off.

Draw the circuit on paper and label it with the voltages you'd expect to see with respect to earth at all the different points.
 
thanks for all the replies, really got myself in a knot with this one!

the voltage showing on the unknown cable (which i mistakinly presumed as live as it was red) varied depending on switch position and which switch, when i measured continuity between this and the known live source this measured around 20-25 ohm, now i have come home and started thinking clearly, im thinking that this changing voltage is actually a floating neutral cable and that the 25 ohm resistance is just the resitstance through the lamps in the circuit which is why it is so high. any objections?
 
by quite alot is there anyway to put a figure on that? the whole house is all on one circuit, would that potentially get it down that low or would we be looking at alot more?
 
Of course there could be other problems, I don't know the resistance of a cold tungsten lamp offhand.

take a cold lamp and measure its resistance and make a note of it
if all the lamps are the same use the proper formula to calculate the resistance total
even if they are different values you can still calculate the total resistance and compare it to your readings.
preparing for a job is more than getting your materials around
set yourself up with a testing regime that covers all bases
this will prevent possible brain farts and make you look good in the eyes of your customers
(impressing them with professionalism is a sure way to get some free advertising)
 
If you have a circuit with the neutral disconnected but line connected then there is no current flowing and so there is no volt drop occurring on the circuit.
Therefore the potential difference to earth at the end of the disconnected neutral will be equal to the supply voltage to earth.
If the neutral were connected then voltage would be dropped over the load and the voltage to earth at the connected neutral would be (very close to) zero.

If you have a resistance of 25 ohms then using V=IR and P=VI you can say that P = V²/R so your load would be about 2.1 kW or 9 A, quite high for lighting but possible.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
having a brainfart......
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--

Advert

Thread statistics

Created
gavin.sibley,
Last reply from
GMES,
Replies
29
Views
2,399

Advert

Back
Top