Suprisingly they've used the cpc for earth. Am I right in assuming they've taken perm feed from a fused spur to give permanent feed to valves along with neutral and earth. Then dropped switch live to jb next to boiler
 
Surprisingly they've used cpc as earth. Am I right in assuming they've used a permanent feed in the loft next to the cylinders then dropped three core down to jb next to the boiler?
 
Surprisingly they've used cpc as earth. Am I right in assuming they've used a permanent feed in the loft next to the cylinders then dropped three core down to jb next to the boiler?

hot water don't need a valve it can be an open loop circuit with a swlive to the boiler if the cylinder stat is in place that's fine,also as previously mentioned the temp on the boiler can be controlled there too.
 
Suprisingly they've used the cpc for earth. Am I right in assuming they've taken perm feed from a fused spur to give permanent feed to valves along with neutral and earth. Then dropped switch live to jb next to boiler
I would assume then that of the 3 cores 1 would be live from roomstat to valve 1 would be from cylinder stat(i think these go to brown on respective valves) then the 3rd core will go from orange linked from both valves which is switched live to boiler
 
The three core from the loft consists of 2 lives and one earth. One of the lives is from the orange and the other connects to s programmer
 
post 32 so they needed 2 cores and used a 3core and earth and used the extra core as earth, sounds like you have a swl for the boiler (orange) and a swl from the programmer which is connected to a cylinder statt or its connected to a room statt.
 