I changed an old fuse board for a new consumer unit and the lighting for this house was connected in two separate fuses. So I swapped one for one and put them into two 6 amp breakers. Now the light at the bottom of the stairs is permanently on and the light at the top is off. Light at top controlled by two way switching. Light at the bottom just controlled by single switch! I think it is possibly one big ring as I am getting cutlrrent on the other when only one is connecting into a breaker?
Borrowed N may be, need to do some investigation methinks.
 
So both lighting cables are live with one disconnected?.....and you think 'it's possibly one big ring'? :rolleyes:
It's two circuits linked in some way. Neutrals/wiring mix up crying out.
Are you getting a return on the disconnected neutral?.....and, if so, under what circumstances?
 
also tested the light that is permanently on and the current is not coming from the switch live but instead from the neutral

How have you established that current is flowing from the neutral?

IR test between the two cir units to establish if there are any interconnections, youll need to do it with all switches closed obviously.

Did the circuits pass all of the commissioning tests?
 