Ze of 0.01!
Blimey you could have some massive PSSC. Probably nothing to do with your problem but that is an extremely low Ze. What's the breaking capacity of the mcbs etc?

You get low readings like that when you don't disconnect main earthing conductor for test.
 
Ze of 0.01!
Blimey you could have some massive PSSC. Probably nothing to do with your problem but that is an extremely low Ze. What's the breaking capacity of the mcbs etc?

Tell me about it, its like 24.1 kA, if to go by mesured 241V, your gear would not handle that, its like 4 times braking capacity of your standard 6 kA mcb, I think you ment Ze=0.10 ohm ....
 
Last edited by a moderator:
Thanks for spotting the type o guys, 0.1 it was, going back for IR tests when he is out.
 
Reading through this thread I noticed there was an issue if the socket on the cooker plate was used under load....Have you considered checking the cooker switch, cooker connection and the actual cooker itself, these things are bad at causing RCD issues..
 