Well gentlemen, the problem has gone away for now but without me finding the solution...
In response to the voltage questions, the fittings that are faulting are on a circuit of 10 lights and only 2 or 3 are faulting - voltage is ok.
The batteries in some of the fittings are brand new - the original fault developed when I was changing the packs after they failed the 3 hour discharge test and I'd had the circuits turned off. As described above by Merl, they flashed twice on restart then wouldn't come back on.
When I got there yesterday most of them had come back to life.
Tried changing the lamps in the remainder to no avail and finally changed the ballasts again and the tinkers worked.
I've returned the ballasts to the supplier and asked to be informed if anythings found...