Have an existing oven circuit 6mm2 twin & earth from the consumer protected by a 32a mcb goes to a cooker control switch, then 6mm2 from the switch was hardwired in to previous oven. Just bought a brand new oven (single oven that fits in cupboard under worktop) specifications are 2.3kW total electric consumption, max cable length 2m, it specifies for the cable type 3 x 1.5mm2 or equivalent.
Is it ok to wire this one the same 6mm2 straight in to the back of the oven?
16A. If the oven has a plugtop on it, you could just terminate the old 6mm to the cooker into a single socket, thus leaving the circuit and fuseboard intact, as well as the oven, as the 13a fuse in the plugtop will provide the protection.
The breaker should be fine for that cable, 32A on 6mm is basically usual for cookers.
Your cooker is a low load since it is just an oven and so long as the connectors on the oven are big enough to take 6mm you should be fine.
Thanks for the quick replies, what size breaker should i size down to?.
For a total load of 2.3 kw, without diversity you could use a 10A MCB.
What does it say in the instruction manual?
If you leave too high a circuit breaker in place, then the oven won't be protected should a fault occur.
BUT.... You could argue that if you hard wire a 1.5mm2 flex into a cooker switch/outlet, then this is part of the circuit so a lower rated MCb will be required to protect the Cable not the appliance
I agree except that he's been told to use 3x 1.5mm cable to connect the oven. If he can't get the 6mm into the oven connections, should we not also protect this bit of the cable too?
The OP asked if the 6mm could go directly into the oven, the 3x1.5mm is the recommended minimum cable size and was not in this case intended to be used.
The circuit terminates at the outlet plate.
Thereafter follow MFI and the appliance, its cables and components will be protected by its own fuses/trips etc
The ovens that I have installed over the years have all stated a size for the MCB based on the load of the unit, this has generally been either 16 or 20Amps.
I am in complete agreement that he should check with the MFI.
I would agree the manufacturers may well have specified a different requirement, with which compliance would be required.
I would have thought most ovens could run on a 16/20A breaker.
However I think we have now lost the OP.
You are wrong.
MCB size is based purely and simply on cable size and installation method.
Sorry to be so arrogant. (Also cant spell)
Reply to Help with Oven Circuit. in the UK Electrical Forum area at ElectriciansForums.net
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
The customer has suggested from a previous electrician that the oven requires a new circuit installed . Upon viewing the instructions it is stated...
Here is my situation We have a dedicated oven circuit in our house with a 40A RCBO We have bought a dual fuel range cooker which states it has a...
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...