So leaving the circuit unsafe is a better option is it? At least the RCD is present and can be tested and certified as such.
1) the RCDs dont work with the circuit connected
2) whoos to say that just putting the offending circuit on an RCBO will give THAT circuit additional protection?....the RCBO may not work due to THAT circuit being fed from it....so how does that comply?!!
 
1) the RCDs dont work with the circuit connected
2) whoos to say that just putting the offending circuit on an RCBO will give THAT circuit additional protection?....the RCBO may not work due to THAT circuit being fed from it....so how does that comply?!!

It doesn't the point was it would need to be tested, if it failed back to square one, if it passed yippee lol.
J
 
i tested at various points throughout the house and the result was always the same with the lighting circuit connected they wont trip.
as you say i know that memshield 2 rcbos wont trip properly up close


I have had a think about Marks problem and have now come to the conclusion he doesn't have a problem :smile5:


With this subject of test procedure in mind
I am aware the test procedure doesn't recommend for circuit loads to be catered for in the test

I have just read the contents of this link,which was found on the IET forum, it seems to give the reasons for no load testing of an Rcd, for anyone interested the conclusion at the end sums it up
http://www.esc.org.uk/fileadmin/user_upload/documents/industry/rcd_research/TaskAEffect of Load.pdf
 
ah interesting
have to say ran auto test so fail at 0deg didnt try 180
however did try x5 manual 0deg

why do you ask
I suspect it's what Des was alluding to earlier with DC saturation. That would only affect one side of the waveform. If it works on one half but not the other then I'd suspect a combination of what Des and spark1973 (possible faulty dimmer/wiring issue (to explain the poor IR)) said earlier.

Edit: In case that's not clear it would need to be a faulty dimmer/switch and the wiring fault (to allow DC from a transformer into the circuit).
 
Last edited:
I suspect it's what Des was alluding to earlier with DC saturation. That would only affect one side of the waveform. If it works on one half but not the other then I'd suspect a combination of what Des and spark1973 (possible faulty dimmer/wiring issue (to explain the poor IR)) said earlier.

Edit: In case that's not clear it would need to be a faulty dimmer/switch and the wiring fault (to allow DC from a transformer into the circuit).

ir fine at time of test readings at start of thread
 
ok so problem solved but not sure how

went back and fitted rcbo to problem circuit and it popped out instantly
when it stayed on long enough it wouldnt trip under test
re tested insulation and there was a n-e dead short 0.0 (this wasnt there before but had suspected intermitant fault)

removed lights and switches and found trapped wire behind light (this light was fitted a long time ago by others)
cleared fault and re tested all ok and rcbo now tripping under test.

can only assume fault was coming and going with expansion and movement in the house in the warmer weather (cant think of any other reason)

so one question remains with no lights turned on and testing at the rcbo why wasnt it tripping under test before the fault was cleared.
 

Reply to help with rcd problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
317
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
780
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
875
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
726
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock