Don't forget if you have more than 10ma leakage (think that's the correct value it's in the OSG anyway) you have to connect the cpcs (if it's a RFC) separate terminals on the cu, and use socket outlets with two earth terminals if it's a radal the the same applies to the sockets and you need to make the cpc a ring. It's all very clear in the OSG but mine is at work and I;m chillin out.
 
Think your mistaken here... the items you have suggested are double insulated are more likely to be SELV where the power plug is the transformer ... this is where the leakage will be generated... Laptops also have a 230v plug with inline DC power supply ... any equipment that externally or internally converts mains AC to DC with smoothing circuitry like computers etc will probably be a source of designed earth leakage.

Where the nature of the DC output dosn't have to be so clean then yes they may be class II like phone chargers where its only used for charging the battery as oppose to running the device.
I take your point, but as an example I have two printers several Routers/Hubs all with A plastic earth pin also all 5 laptops I have (2 dell 3 Toshiba) all have figure 8 leads on them, although IIRC one of my old ones did have a 3 pin lead to the PSU. I cant actually find any pieces of IT equipment other then the desktop PCs that have an earth pin, not saying that its typical of all IT equipment particularly commercial stuff such as large printers and switches which obviously do generate leakage however in a domestic environment I would be surprised if leakage from IT equipment is ever really a problem
 