Hi All.

I had a job which was going to be a 'quicky' fault finding and repairing a couple of sockets, then it came to the testing.....

The consumer unit gave me no cause for alarm but was all labelled up wrong, so it turned out there were far more sockets and square meterage on this ring final than I first thought.

So I get, on end to end continuity (2.5/1.5 T&E)
r1=1.41 ohms, rn=1.43 ohms, r2=2.38 ohms. Then from that fig 8 test a range of R1+R2 from 1.53 to 2.61 ohms.

Way too high. Nulled the leads (again). Checked again...

If it was just one of those end to end readings that was too high, I would set about looking for a high resistance connection, but as the r1 is so similar to rn and the r2 is about right too - it seems unlikely that there is a high resistance joint in all three?

If I reverse input those readings to get a estimated cable length it comes out at around 190 metres!

The house is not particularly old - about 10 years I think. The floor area of the circuit is round about the 100 square metre mark, maybe more, and includes ground floor and first floor rooms - so the cable length could well be pretty high. On the limits at guess - but not way over as I have found.

Splitting this all down would be no easy task, and I've been told the wiring was 'inspected' three years ago during a change of ownership. So I'm looking to avoid the disruption, if possible. If anyone has any advice or ideas I'd certainly appreciate it - big time.

Are there any factors which might have given me misleading high readings?
 
Max Zs is 1.29 ohms on a B32. Correct for temperature I usually work to 1.10. So no - disconnection times not met.

Mountain out of a mole hill? I thought disconnection times were there for a reason - I mean how do I write it up. Is it not in -unsafe condition?
 
I assume it's on an RCD? Bs 7671 permits an RCD to take care of earth fault protection on a TN system, in which case your max Zs becomes 1667 ohms. I'm not saying that would be usual practice, but this is a circuit only marginally over required criteria. I just cant see the point in major disruption and expense for a circuit like this. Alternatively loadings permitting, stick it on a 20a OCPD
 
Max Zs is 1.29 ohms on a B32. Correct for temperature I usually work to 1.10. So no - disconnection times not met.

Mountain out of a mole hill? I thought disconnection times were there for a reason - I mean how do I write it up. Is it not in -unsafe condition?
I assume it's on an RCD? Bs 7671 permits an RCD to take care of earth fault protection on a TN system, in which case your max Zs becomes 1667 ohms. I'm not saying that would be usual practice, but this is a circuit only marginally over required criteria. I just cant see the point in major disruption and expense for a circuit like this. Alternatively loadings permitting, stick it on a 20a OCPD[/QUOTE
 
It's up to you to determine whether it's safe, your name on the form, I'm just saying what I'd do. Regarding the 30/32a device for a ring final, if you feel the load is OK for a 20a then put it on the form as a departure and justify it with the reason you've given that it is a poorly designed circuit and reducing the OCPD rating is making it safer.
Personally I'd list the high circuit readings on the form with explanation, leave it on a 32a and state that the RCD is meeting disconnection times and that I consider the circuit poorly designed but safe for continued use.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sheffield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
High r1, rn, r2 etc on ring final.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Marcus Vaughan,
Last reply from
Marcus Vaughan,
Replies
20
Views
11,995

Advert

Back
Top