- Reaction score
- 5,607
I have just been asked to provide power to a large garage/workshop for a friend. The workshop is approx 55m away from the main CU and there will be a further run of approx 15m for the lights from sub board to end point of lighting circuit. It will be on a 32A MCB in the main CU. measured voltage at the time was 247V
The transformer supplying the property is approx 100 - 200m away.
I dont have all my calculations to hand but that isn't really the point of the thread. The point is 'Do you stick rigidly to VD calculations and always base your cable size on these results?' (I'm assuming all other requirements are met, i.e Zs, acceptable reference method etc).
Basically lets say the VD works out to about 8V on the lights using 10mm SWA and 1.5mm T&E for the lights, this is above the 6.9V limit. I feel 10mm is acceptable, would you use 16mm? It just seems a bit crazy to oversize this cable in the really, really unlikely event VD will ever be a problem. I'd be greatful for some real case examples from the experienced guys and whether they always stick to the 3%/5%?