Lucien Nunes
C2 for the fused neutral but in a way it's only 'potentially potentially' dangerous. Until it blows, it does no harm to anybody and might just as well be a solid chunk of brass. As it can only blow due to overload, not earth fault, in many situations it's unlikely ever to blow. If it does, it's still no more dangerous than a broken connection in the neutral which poses no risk to a sensible person who isolates the circuit to investigate. Only someone blundering in assuming the circuit is dead without isolating or testing will get stung by the 'dead but still live' circuit.