How would you do earth continuity on ring circuit in two core MICC cable?
 
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
Aico 3000
littlespark

littlespark

-
Esteemed
Arms
same as you would with any metallic containment such as conduit.
 
littlespark

littlespark

-
Esteemed
Arms
I’ve edited my post and removed that.
which test are you doing? Initial verification or periodic?
 
littlespark

littlespark

-
Esteemed
Arms
It’s only the live conductors that need to be proven to be in a ring configuration. The cpc just needs the continuity to be verified between the sockets and the MET

is the micc not in a ring? Or are the cables touching?
 