Hi,

To calculate the voltage drop of a cable from Appendix 4 of the IEE Regulations we use the following formula:

actual voltage drop = factor x load current x length
1000

My question is that i tried to solve some problems regarding the current capacity of cables from electrical installation books. It was said that a 2 kW heater at 230 V is installed 30 m away from the consumer control unit. I am confused about what length i have to take whether the 30 m or 60 m, the latter to take into consideration the length of the neutral conductor also. The book solved the problem with the 30 m length.
 
its just the length of the cable run, so if its 30m away, then its 30m.

we dont 'add on' the neutral length, because its the voltage AT the appliance that we are concerned about, not the voltage that 'returns'

and the V that hits the appliance on the line conductor, could be 235v, could be 230V, could be 225V - doesnt matter, because on the other side of the 'load' (on the neutral) it will be zero, regardless of what it was to start with

hope that helped
 
Voltage Drop on dc supply

As it was already said on ac supply the voltage drop on the neutral conductor is not taken into account when calculate the permissible voltage drop, since it is at zero potential in TT system.
What about if the system is dc instead, do we need to take into consideration the resistance of both conductors (+ and -) or take the resistance of the positive conductor only to calculate the voltage drop in cables.
 

Reply to IEE Regulations Voltage Drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock