Discuss Immersion heater and central heating on same circuit? in the Australia area at ElectriciansForums.net
Install a single socket and put a plugtops on the immersion heater flex and boiler feed.
That way only one can be used, you don't normally need both on at once anyway.
Gas being cheaper than electricity the immersion is usually only used in an emergency.
1, I don't like immersion heaters on plug tops.
2, I wouldn't have both methods of water heating on the same circuit, as a fault in one could knock out the other.
3, The immersion heater is quite a large load, and it is recommended that such loads are placed on separate circuits.
Put them both on a 20 amp radial - immersion fused at 13 amps ( hope i`m not gonna start another row here about running 13 amps through a 13 amp fuse) and CH at 3 amps or 5 amps as required
Strangely enough it seemed to be a common practice to wire an immersion heater from a ring main circuit in the 1960s using a switched spur unit for isolation.
I have seen a quite a few overheated fuse holders over the years !
Personally I tap Immersion heater circuits quite a bit, cos they never get used anyway. Imm heaters about 12.5 amps and a 2.5 radial can go on a 20amp MCB so not really a prob load wise.
20 dp switch for immersion heater and dp sw fused spur @ 3a on a 2.5 radial would satisfy loading but why would you want to run 2 2.5 radials? Personally i would never run an immersion on a sw fused spur
I have never seen an Immersion on anything other than a SFS. It is after all a 13 Amp fuse, surely theres a reason that all imm heaters draw almost exactly 13 amps
Although many existing immersions have a swFCU. Often on a 15A 3036. I'd leave it as is unless there's a problem, but would install a 20A DP by choice.
99% of domestic ch systems will pull less than 1A - it's the pump that's the large consumer and these are rarely more than 150W. So, CH and immersion on a 16A mcb should present no problems. Both should have DP isolation (remember most FCUs are SP).
It was usual in the 60s to fit a small square 20A DP sw.
In the villages round our way where there is no gas people tend to use immersions rather than oil for hot water. I've come across many burned out swFCUs. Always replace with 20A DP sw.
Reply to Immersion heater and central heating on same circuit? in the Australia area at ElectriciansForums.net
Can I supply my central heating (programmer, two port valves and boiler) via a fused spur taken from the immersion heater circuit? They’re...
I need a 3 phase immersion heater with a DN32/42 mm thread for a commercial pasteuriser. The only ones that I've found so far are not inexpensive...
How would you go about this realistically, the office is open plan and about 15m x 7M, grid ceiling with loft space above, windows and insulation...
I've purchased a horizontal unvented cylinder that has come with 2 immersion heaters. I was hoping to use the same circuit the my existing tank...