I guess wirepuller, we are going to have to disagree on this.
The Regulations require all extraneous-conductive-parts be bonded. List of examples is provided in 411.3.1.2.
This list includes the metallic sheath of communication cables, but indicates that consent should first be obtained from the owner/operator of the cable.
Considering that with BS7671, safety is paramount and if the position of the connection would have any impact upon safety.
I find it very hard to accept that any restrictions would be placed on where to make such a connection on the basis of who owns the pipework.
If safety can be improved by placing the connection before the meter at a point closer to where the pipework enters the building, then that would be a requirement with the proviso (as with communication cables) that consent is obtained.
BS7671 also allows pipework (with certain conditions) to be used as a protective conductor.
One of the conditions is that electrical continuity is maintained, another being precautions being taken against removal.
To my mind such conditions can be met by compliance with 544.1.2 i.e. by making the connection within 600mm of a meter, to hard pipework and before any branch pipework.
Bearing in mind that it is a requirement for every connection (with certain exceptions) to be accessible for maintenance I cannot see a problem with making the connection where the pipework becomes accessible, rather than hidden away in an inaccessible position under the floor boards.