Hello Forum,

I need to replace the hob in the kitchen as it is faulty.

I would like to be able to use an induction hob, so I need to make sure that the wiring and mcb on the cooker circuit is the right specification.

The combination Oven (1 small / 1 Large ) has a Max load of 4.1Kw.

The induction Hob has a Max load of 7.35Kw.

So that is a total of 11.45Kw.

The cooker circuit is on a 32a mcb.

The wiring is all 6mm T&E, a single cable goes from consumer unit to isolation switch, then splits into two 6mm cable, one to the oven, one to the hob.

It is a new build with all wiring hidden behind plasterboard walls and plasterboard ceiling.

From what I read, it appears that the 32a mcb and the 6mm cable is of adequate specification.

Obviously I want to make sure all is safe, so could you confirm this or advise what needs to be upgraded?


Thanks in advance


Richard
 

Wilko

Electrician's Arms
Messages
5,490
Location
Berkshire
Hi Richard and Welcome.
The 6mm and 32A mcb are the normal for domestic cooker circuits. Design wise they are likely to be ok for what you are proposing, based on the fact that not everything is on and demanding full power at the same time. That said, if I was installing for you I’d be closely reading the manufacturer’s installation instructions and inspecting and testing the existing circuit.
 
OP
H

hallra

New EF Member
Messages
3
Location
London
Hello Wilko and thank you for replying to my post.

As you have confirmed, which was my understanding, is that the cooker circuit is a standard U.K. design/specification.

With it being the standard design specification, I would hope that it is perfectly safe to use and the worse that can happen is if too much demand is place on the circuit is that the consumer unit would trip?

Thanks again in advance.

Richard
 

cliffed

Regular EF Member
Messages
1,239
Location
Lancs
It’s down to the load,with diversity should be ok.
If you were originally installing 1st fix you might be inclined to put a 10 mm in,but 32 amp,it’s ok..like wilko says.
 
OP
H

hallra

New EF Member
Messages
3
Location
London
Thank you both for your replies.

I agree, if it was a new brand new install then, 10mm would be preferable.

With it being a new build, with the methods of construction and the location of the Hob to the consumer unit, I don’t see an easy way to feed a new cable without a huge cost.

So the best thing I see, is to use the current cooker circuit and only install a new circuit if the current proves to be problematic when in use.
- Hence the only thing I wanted to check was that the safety components would protect in the event of an overload.
- I understand that overload protection has been part of Building Regs since mid 2000s...

The worse that can happen is a trip at an inconvenient time, which with only me and the misses is very unlikely, we don’t tend to have banquets:)

Thanks again

Richard
 

telectrix

Disrespected Scouser
Electrician's Arms
Trainee Access
Messages
63,525
Location
cheshire/staffordshire
can't see any problems with your current set-up. 6.0mm cable on a 32A MCB has always been good for cooking apploiances to a total rated load of 15kW.
 

shaun1

Regular EF Member
Messages
248
Location
United Kingdom
Overload protection has been part of the wiring regs since lomg before the 2000s. You are correct that the MCB should trip on overload, but you also need to make sure the connections are done properly in a suitably rated outlet plate. As these can overheat if done badly, particulalry with the higher current.
 

GeorgeCooke

Regular EF Member
Messages
556
Location
UK
I agree, if it was a new brand new install then, 10mm would be preferable.
No that would be a waste of copper and waste of money. Even 6mm is over the top. It is a 32 amp circuit and all that is required is 4mm cable. The purpose of the MCB is to protect the cable not the appliance on the end of it.
 

Paignton pete

Regular EF Member
Messages
978
Location
Over the rainbow
No that would be a waste of copper and waste of money. Even 6mm is over the top. It is a 32 amp circuit and all that is required is 4mm cable. The purpose of the MCB is to protect the cable not the appliance on the end of it.
Agree totally.
Too many installers go over the top with cooker circuits.

If you go to the time to work out actual cable calcs 4mm would normally be enough. Sometimes 6mm. I’ve never needed 10 mm, but seen it done too many times.

Hi hallra, your set up is absolutely fine.
 

telectrix

Disrespected Scouser
Electrician's Arms
Trainee Access
Messages
63,525
Location
cheshire/staffordshire
you total load is 49.78 A. round it to 50A,
the rules for diversity on a cooking appliances are:

10A + (30% of remainder) 12A = 22A ( add 5A if a socket is incorporated ).
so 6.0mm on a 32A MCB is perfect.
 

GeorgeCooke

Regular EF Member
Messages
556
Location
UK
you total load is 49.78 A. round it to 50A,
the rules for diversity on a cooking appliances are:

10A + (30% of remainder) 12A = 22A ( add 5A if a socket is incorporated ).
so 6.0mm on a 32A MCB is perfect.
22+5 =27 which just happens to be the rating of 2.5mm cable.

However because it is on a 32a MCB we need to use 4mm, no more.
 

davesparks

Mentor
Electrician's Arms
Trainee Access
Messages
13,305
Location
guildford
22+5 =27 which just happens to be the rating of 2.5mm cable.

However because it is on a 32a MCB we need to use 4mm, no more.
without knowing the route and which rating factors apply how can you be so certain of the cable size? bearing in mind its a new build there will be plenty of insulation around the place.
 

Paignton pete

Regular EF Member
Messages
978
Location
Over the rainbow
I always apply diversity to the separate appliances, in this case hob & oven. Which still would be fine I would suggest.
Agree

As there are 2 appliances I would say

First 20A then 30% of remainder(9amps) total 29A

Plus 5A for socket 34Amps

The 6 mm cable in place is fine. The Mcb’s would then be 40A

I would also say the 32A Mcb’s would be fine as a bit of common sense adjustment calculations on diversity from the designer.
 