Good morning everybody,

I’ve been asked to look at a job to install a 3 phase compressor in a body shop.

It is a 3 phase 20a machine which is fine, the only issue is the lay out.

The consumer unit and compressor are sitting outside the workshop but the mechanic has asked if I could put a switch inside that controls it (the unit is fairly big and I understand he doesn’t want to keep walking outside to turn it on / off).

Now I’d normally just put a 3 phase isolator next to the machine and be done with it but is there a way he could have a local switch to him that turns it on / off?

all the best, ET
 
just add a second isolator in series, or even a stop button if the control circuit for the compressor has the facility
 
Good morning everybody,

I’ve been asked to look at a job to install a 3 phase compressor in a body shop.

It is a 3 phase 20a machine which is fine, the only issue is the lay out.

The consumer unit and compressor are sitting outside the workshop but the mechanic has asked if I could put a switch inside that controls it (the unit is fairly big and I understand he doesn’t want to keep walking outside to turn it on / off).

Now I’d normally just put a 3 phase isolator next to the machine and be done with it but is there a way he could have a local switch to him that turns it on / off?

all the best, ET
Where is the starter installed?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Watford
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Heavily Qualified Electrician / Teacher / Tutor - etc

Thread Information

Title
Industrial question
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
ETradesmen,
Last reply from
R-fur,
Replies
4
Views
798

Advert

Back
Top