Hello folks, I have just finished installing a WarmUp DWS600 loose wire system in my bathroom.

A little more on it here, but essentially it's rated at 0.6kW / 2.6 amps.

Warmup DWS 600 Loose Wire Underfloor Heating Kit - http://www.directheatingsupplies.co.uk/warmup-dws-600-loose-wire-underfloor-heating-kit

How should it be fused? Would a switched fused spur with a 3 amp fuse be ok for this / any reason why I should not?

http://www.builderdepot.co.uk/bg-ne...ction-unit-with-neon-brushed-steel-fbs52.html
 
Yep, 3A is fine, but must protected by a 30mA rcd/RCBO if it's in a bathroom ( use an rcd fused spur if the circuit is not already rcd protected).
 
what he said ^^^^^.FCU on wall outside bathroom. stat. next to it.
 
Morning folks thanks for the replies. I will check on the fuse board at home if that particular circuit is protected by a 30mA RCD and report back. Fingers crossed it is!
 