Why does he need to take responsibility for the existing CU in the garage? I would just record the tests for the new feed/armoured, and put "Rewire of house and new CU only" on the cert? Test it by all means but it would be a separate job unless it was covered in the original quote?
I agree
 
I was just unsure as I've altered the characteristics of the supply to the garage CU so would it need a certificate for the circuits that run off of that CU or is the circuit supplying it being on the EIC sufficient
 
FWIW I would show db2 on the cert and do a random Zs on the socket circuit. Note that in the description....
 
What if you replace a board in a factory, rewire submains from it to existing boards which in turn then supply 400 existing circuits, you going to test the lot, I think not.
 
It wasn't part of the original agreed works so the only thing I was thinking to get around doing any works to the garage or issuing a separate schedule of test results was to agree with the client that it would not be included and go down as a limitation?

Limitations are for EICR's not EIC's.
Results for the existing installation aren't required but for what it's worth, after a full rewire, what's the problem with a bit more testing and a further set of schedule and results?
 
Limitations are for EICR's not EIC's.
Results for the existing installation aren't required but for what it's worth, after a full rewire, what's the problem with a bit more testing and a further set of schedule and results?
Doesn't belong on the EIC, doesn't form part of the works carried out.
 
what does the garage wiring look like ? is there any test certs for garage if all seems ok test up to garage D.B. maybe loop at socket and light.Make sure that it is put on the electrical certificate new sub-distribution circuit to garage only.
 