SKY
Hi Chaps
I'm moving soon to a new house thats more in the country and does suffer a few power cuts in the winters as its over head lines.
I'm thinking of installing a standby generator so that at least we can have lights and basic power upon a cut -looking for a small Honda unit maybe 5KVA
I would like to install the genny in the garage at the bottom of the garden and would be running 6mm SWA to the garage anyhow for power so I can run generator feeds at the same time.
I don't really want auto cut in and would like to start it myself in the case of a power cut.
What do I need to do to install this and what provisions do I need to take?
Thanks All - Never done a genny before so want to learn!
Lots of safety and electrical system separation issues to cover there, too much really for a forum answer,(and I do not know enough anyway!)
You need to determine your method of earthing, your installation of a changeover switch, RCD protection for all circuits, the method by which you ensure that you generator does not connect in any way with the grid, that your generator provides a stable output for the item you wish to power.
Section 551 of BS7671 covers generating sets.
The ECA issued this for mobile buildings (not all relevant)
View attachment eca mpba guidancev2 earthing mobile buildings-133331.pdf
2011 39 summer wiring matters did a bit on portable generators (again only tangential).
too big to load here but you may be able to find it online.
Hopefully you may get more response later.
Hi Chaps
Well for a kickoff, most small portable generators are not recommended for use to supply a domestic installation. They will in fact stand a good chance of destroying anything with sensitive electronics incorporated, such as PC's, Laptops, TV's etc etc.... Virtually none of these small gensets will incorporate any form of stable Voltage Regulation, voltage only being related to speed, and will also be of a floating earth arrangement!! These small generators are basically only any good for supplying site based tools and the like!! So DON'T be tempted to use such a unit, it could cost you a lot more than the unit itself!! lol!!
So you're first exercise is to find a suitably rated standby generator that incorporates a means of voltage regulation, and can be suitably earthed/grounded. You'll be looking at units around 8 to 10 KVA, though i have seen a 6 KVA unit with a voltage regulation module, but i think you'll be looking at units that going to be getting close to £1000 mark to be honest!!! If you're still interested, then we can guide you through the installation requirements associated with a generator standby supply to a domestic house....
As i stated earlier to have a domestic stand-by generator that incorporates any decent form of AVR, will be getting close to the £1000 mark, and that's before you start thinking about any MTS/ATS and controls or other associated installation costs. It can be an expensive business having an alternative stand-by power facility!!