applesandppears
I would say this guys a numpty but needs a kick up the --- with some help?
I would expect a high resistance reading greater than 2 mega ohm, certainly not under 1 mega ohm?
Possible reasons for this would include damaged insulation, or a load connected.
Though my (clearly inferior!) brain can't see why is you have a live and neutral at the same potential difference going to earth then there should be a high resistance reading unless the voltage is arcing through line conductors to earth?
Shall I just stick the probes to my brain to stimulate it maybe? 1kV!
I would expect a high resistance reading greater than 2 mega ohm, certainly not under 1 mega ohm?
Possible reasons for this would include damaged insulation, or a load connected.
Though my (clearly inferior!) brain can't see why is you have a live and neutral at the same potential difference going to earth then there should be a high resistance reading unless the voltage is arcing through line conductors to earth?
Shall I just stick the probes to my brain to stimulate it maybe? 1kV!