I would say this guys a numpty but needs a kick up the --- with some help?
I would expect a high resistance reading greater than 2 mega ohm, certainly not under 1 mega ohm?
Possible reasons for this would include damaged insulation, or a load connected.

Though my (clearly inferior!) brain can't see why is you have a live and neutral at the same potential difference going to earth then there should be a high resistance reading unless the voltage is arcing through line conductors to earth?

Shall I just stick the probes to my brain to stimulate it maybe? 1kV!
 
trev - yes it is possibly the blondest moment i've had for a few years. I'll die my hair back after i've cleared this up!

telectrix - thank you!

Considering the installation is relatively new (2004 good condition, visually) it seems very likely be that PME on the TN-C-S supply.

In anyones experience could it be damage anywhere? as this low resistance would surely cause a form of arcing on a 32A?
 
If you can not access whole house what are you doing testing it !! You don't know what runs where and whats still connected. Go back when you have access to whole house, if you don't how can you be sure whats in the rooms the other rooms.
 
its addition of a couple of sockets. Minor Works

Zs acceptable
Polarity acceptable
IR.........................planning to test live and neutral on circuit connected together (one probe) then down to earth (second probe) (with neutral disconnected to bypass PME) would this not be ok regardless of whats on the circuit?
 
I would never extend a circuit when I can not check whats on it and never test it without having full access. Maybe just me
 
Disconnect everything mate that way you know the circuit is isolated from anything that can affect your results. Recheck everything from square one.
You're most likely going round in circles and disappearing up your own butt, go back to it tomorrow and start from first basics and I'll bet you sort it in minutes.

- - - Updated - - -

As iconnect says, that's the way forward
 
i'm as rusty as a nail exposed to a rust

thanks, will clear up tomorrow and thanks for pointing me in the right direction. Appreciated

peace
 