Okay, lets get the ball rolling. What is the minimum circuit insulation resistance required between L and E according to the regs.....or even according to your college notes?


The minimum IR according to reg is 1M ohms
 
The minimum IR according to reg is 1M ohms

Okay, according to your question you have an IR of Live to earth = 0.75 M ohms. Obviously 0.75 is less than the required 1Mohm so we know it's not acceptable, the remaining question is 'state the actions to be taken?'
 
just don't use an rcd, falsify an acceptable result on a test sheet, take the money and get out of there. jobs a good'un
 
0.75 is not acceptable so I would start by checking the circuit looking for any joints or cable damage, maybe there is something connected outside that is open to the elements? Buried under ground? As a student myself I come here for a lot of information and these guys are good at helping but you have to appreciate they had to learn themselves and in order to get a little you have to give a little. ..
 
do they actually refer to it as testing between Live and Live these days then?

not happening around me, far too confusing.

The easiest way to answer an ir testing exam question is to state 'test between all live conductors and all live conductors and earth. Saves loads of writing and saves the examiner loads of reading, also less chance of losing a mark for a silly mistake in a more detailed explanation, so I was taught.
 