• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss IP rating of Nylon cable gland in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Amaccc

-
Reaction score
0
Hi guys
New to this forum and thought I’d ask the powers to be on here for some advice.
Basically I’m on a job installing some electrical instruments. The instruments are quite small and have come with the gland body , lock nut and ip washer on the outside . The reason for this is to reduce the entry thread for obstructing the terminations inside the device as it is very small. My question is, does this effect the Ip rating having the lock nut hard up against the main gland body on the outside ?

Thanks folks IP rating of Nylon cable gland EE0A47BB-776C-4677-8EDE-74956116769A - EletriciansForums.net
 
If you are trying for IP 67 or 68 then it’s unlikley to seal well enough because water can creep down the thread.

You would be better to cut the thread length down on the fitting and use a flat sealing washer.
 
Hi Guys .
Thanks all for your reply’s . Decided to remove the lock nut.A few reworks required on a couple that’s been terminated already but the best solution going forward.
Thanks again
 