Hi guys,
did a cu change in an indian takeaway,fighting the clock,split the ring and thought i had the prob sorted so put socket back on then got 0 reading did this with a few sockets, they were old and pretty gunged up do you think this was the prob off back tomorrow with four new sockets also cos its a small place with one ring i was struggling to suss how it was wired,any thoughts.
 
Likely there is a load in the circuit you havn't identified. Try removing the sockets you are suspecting and put temporary connections in their place.
Then re-test.
 
I think the extractor fan system is run off the ring cos it wasnt working and i didnt realise till the owner said the fans not working as i was leaving
 
Likely there is a load in the circuit you havn't identified. Try removing the sockets you are suspecting and put temporary connections in their place.
Then re-test.

Wago's are the dogs for doing this. I had a line to earth short circuit on a kitchen ring on Monday, turned out to be a very cheap poor quality chrome socket that someone had got in a lucky bag for about 10p.

Cheers.......Howard
 
was this line to earth or line to neutral? i normally just do a quick continuity check line to neautral, if you get continuity generally there is still a load somewhere, join the line and neautral together on one leg at the board then test line+neautral together to earth, see if its any better.
 
you could always do a continuity between the cpc and N and L and cpc this will confirm you've not got a short to a back box some where ,if ok do as keith has said it could be as been said an appliance still plugged in , dont forget to re do your IR tests if you do find a fault or appliance plugged in

Nick
 

Reply to IR fault on ring in the Australia area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone, Hope everyone is keeping well. At a property Fault finding prior to consumer unit upgrade. Amazing that some bright spark thought it...
Replies
1
Views
2K
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock