With the introduction of electronics into socket outlets and other devices. IR testing has become very laborious, I am only talking about EICRs, I spend more time looking for possible causes for low readings than anything else.
From another forum I gathered there was talk of doing away with the IR test.
What are your thoughts on this.
 
My take on it is it is an ingenious method of assaying the state of cables in an installation. I eschew the global LN to E as I feel it is a very incomplete test and like to get into the installation more and know exactly what is going on. I am sure that is heresy but that is just me, curious and really want to be sure that when I say a circuit is safe to keep in use I know it is. I know there are instances where that is just not practical but still I will gravitate toward L-N L-E N-E where I can and yes I keep the earth in the earth bus bar!
 
I only ever do IR L-L and L-N on initial verification. It is too disruptive and unnecessary for an existing install.

As far as testing periodically, For the breakdown to occur between those it would require 2 faults, which if there is a path between them, almost certainly there is a path to earth which you can pick up on LN-E test. That's would guide you to investigate further.

Cliffed. That's is soo true lol. All these 299 readings we see, which you know haven't even been tested due to what would of had to have been disconnected to achieve that.
 
I only ever do IR L-L and L-N on initial verification. It is too disruptive and unnecessary for an existing install.

As far as testing periodically, For the breakdown to occur between those it would require 2 faults, which if there is a path between them, almost certainly there is a path to earth which you can pick up on LN-E test. That's would guide you to investigate further.

Cliffed. That's is soo true lol. All these 299 readings we see, which you know haven't even been tested due to what would of had to have been disconnected to achieve that.
I'm going to take that sage advice, as I like the sound of it.
 
My take on it is it is an ingenious method of assaying the state of cables in an installation. I eschew the global LN to E as I feel it is a very incomplete test and like to get into the installation more and know exactly what is going on. I am sure that is heresy but that is just me, curious and really want to be sure that when I say a circuit is safe to keep in use I know it is. I know there are instances where that is just not practical but still I will gravitate toward L-N L-E N-E where I can and yes I keep the earth in the earth bus bar!
Great to see the English language used so eloquently. Your line , “I know there are instances where that is just not practical” sort of puts it back to having to use L&N to E method, which increasingly is the case.
 
In the 'old days' before the widespread use of switchmode power supplies (chargers, PC power supplies, LED drivers etc) you could do an IR test and if you did a leakage clamp test around the supply live and neutral the results of both tests would tally.

Nowadays an global IR test gives little or no indication of leakage (functional or fault).

I'd only see the value of an IR test if you're fault finding or as a dead test on a new installation or circuit.
 
In the 'old days' before the widespread use of switchmode power supplies (chargers, PC power supplies, LED drivers etc) you could do an IR test and if you did a leakage clamp test around the supply live and neutral the results of both tests would tally.

Nowadays an global IR test gives little or no indication of leakage (functional or fault).

I'd only see the value of an IR test if you're fault finding or as a dead test on a new installation or circuit.

I am coming around to that way of thinking as someone mentioned you often see 299MΏ on a EICR and you just know it's false.
 
Nowadays with TPN boards filled with RCBOs IR testing is becoming a right headache. Disconnecting individually from each RCBO rather than a global test
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Swansea
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Michael Jones Electrical Inspection

Thread Information

Title
IR Testing what is your take on it?
Prefix
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
12

Thread Tags

Tags Tags
testing

Advert

Thread statistics

Created
Michael J,
Last reply from
BLBelfast,
Replies
12
Views
2,412

Advert

Back
Top