Saw videos on YouTube showing MFT's and DMM's used for testing equipment. Would these produce valid results considering the complicated array of adapters required
 
They will produce valid results, if you know what you are doing. Dedicated PAT testers are better if you are doing a lot of testing. Many of them will store the test results for later production of reports.
 
Not sure about all dedicated PAT testers, but I seem to recall that the one my company purchased could only test IR at 500V. Not good for some equipment such as battery drill chargers.
You may be able to find a list of equipment that should not be tested at 500V on line?
 
You dont need any of the adapters that they sell to use your mft for this, all just money making, the only "essential" tests other than visual are insulation resistance and earth continuity. Both can be done by a MFT just fine with probes and croc clips.

As others have said PATesters tend to have additional functions, earth leakage for example, save, etc etc, guess it depends on your requirements
 
Agreed, power supplies for one. The "clean earth" circuit provided for computers prevents their functional earths affecting other circuits in the installation.
I have a decent mains powered PAT tester that checks, amongst other things, Touch leakage, Substitute leakage and Differential leakage. Earth testing equipment properly is important.
My thread poses the axiom, can you test equipment properly with an MFT?
 
Danny your £25 PAT adaptor can be made for pennies with an extention lead socket and a couple of banana plugs. If someone owns an MFT they should know whether insulation or continuity readings are satisfactory. If not then they only need a simple tester like Seaward 50 that shows "Pass" and "Fail"
 
Risteard non of the so called "proper" hand held battery powered PAT testers can provide 25 Amp earth bond current
I didn't say they could. I didn't advise using a battery tester.

The 25A Earth bond is important. 200mA is an almost useless test.
 

Reply to Is a dedicated PAT tester required or can it also be done with an MFT? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
626
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
561
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Replies
0
Views
251
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
612

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock