Like you say, there are many issues present, but: the 3m rule isn't a reg
Just to clarify, I wasn't meaning DNO rules about tail lengths.
I was talking about the stuff in section 433 regarding position of an overcurrent device, which does mention 3m. (The same bit that allows you to run small conductors from a bus bar chamber to a switched fuse in certain circumstances). Not a regularly cited reg for sure but it's there.

But we unsurprisingly agree that whatever the finer points are it's not up to scratch!
 
There are several issues there but head and shoulders above the others is:
-Supplier fuse is OCPD device for a sub-main (which presumably exceeds 3m) (questionable CCC)
-lack of earthing/correct installation of SWA
-single insulated conductors accessible
Also, the DNO won't like the actual meter seal being cut, he probably was able to wriggle the head fuse carrier out as the top seal has a lot of play that's if he bothered pulling it.

Yeah, don't worry mate I'll sort it jobs a good un.
Happy days.
 
Last edited:
Just to clarify, I wasn't meaning DNO rules about tail lengths.
I was talking about the stuff in section 433 regarding position of an overcurrent device, which does mention 3m. (The same bit that allows you to run small conductors from a bus bar chamber to a switched fuse in certain circumstances). Not a regularly cited reg for sure but it's there.

But we unsurprisingly agree that whatever the finer points are it's not up to scratch!
I agree depending on what's on the end of the Swa and the length at least regarding overload it could be compliant.
 