Discuss Is this a Part P failure? in the UK Electrical Forum area at ElectriciansForums.net
I'd say its a bit more than that.
There is no way the distribution circuit (armoured cable install) is compliant with the regs (BS7671) in many ways and its more than a deviation as (my understanding) deviations are permitted if no less safe than set out in the regs. This clearly is not and an installation certificate nor a building reg (Part P) certificate should ever have been issued.
I was told as a first year apprentice that you can't issue an EIC if there are any no compliances
The best the builder could issue is a EICR with a C2 for the Sub-main
Like you say, there are many issues present, but: the 3m rule isn't a reg
Just to clarify, I wasn't meaning DNO rules about tail lengths.
I was talking about the stuff in section 433 regarding position of an overcurrent device, which does mention 3m. (The same bit that allows you to run small conductors from a bus bar chamber to a switched fuse in certain circumstances). Not a regularly cited reg for sure but it's there.
But we unsurprisingly agree that whatever the finer points are it's not up to scratch!
There are several issues there but head and shoulders above the others is:
-Supplier fuse is OCPD device for a sub-main (which presumably exceeds 3m) (questionable CCC)
-lack of earthing/correct installation of SWA
-single insulated conductors accessible
Also, the DNO won't like the actual meter seal being cut, he probably was able to wriggle the head fuse carrier out as the top seal has a lot of play that's if he bothered pulling it.
Yeah, don't worry mate I'll sort it jobs a good un.
Happy days.
I agree depending on what's on the end of the Swa and the length at least regarding overload it could be compliant.
Reply to Is this a Part P failure? in the UK Electrical Forum area at ElectriciansForums.net
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
I have an electric oven - now many years old. I have replaced the main circular 2.5kW oven element (ELEHY6708) several times over the years...
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...