One of these along with one of these can fit into a single gang 3 grid front - so if you can tap into the wiring before it gets to the switch that covers things.Thanks thats great! Yes earthing was ommitted for diagram. Click mode gride switch. Need to look into that to.
Thanks for all your help . Much appreciated.One of these along with one of these can fit into a single gang 3 grid front - so if you can tap into the wiring before it gets to the switch that covers things.
If not, then you can get the isolator and 2 fused spurs into a two gang front
Just depends which is easier in the circumstances really - if there is RCD protection on a local socket circuit but not the lighting then the switched FCU method as you've drawn is a neat way to ensure the required RCD protection on the fan and bathroom light.
Is this fused spur RCD protected ok to install in bathroom safe zone? Morning.Thanks for all your help . Much appreciated.
Also is it safe to run surface mounted pvc trunking in zone 2 in the bathroom?Is this fused spur RCD protected ok to install in bathroom safe zone? Morning.
Any of the 'standard' fittings like this are regarded as IP20, which can't be used in zone 1 or 2 (so up to 60cm from the side of the bath). Outside of that they are ok for general use in a bathroom as long as they are not likely to be sprayed with water.Is this fused spur RCD protected ok to install in bathroom safe zone? Morning.
Thanks for the advice . No RCD protection in the property. I also have the option of placing the RCD Spur outside the bathroom . I think from the edge of bath to wall is around 35 - 40 cm.Any of the 'standard' fittings like this are regarded as IP20, which can't be used in zone 1 or 2 (so up to 60cm from the side of the bath). Outside of that they are ok for general use in a bathroom as long as they are not likely to be sprayed with water.
PVC trunking is OK in zone 2 to run cables through, though it shouldn't have any joints within it as it doesn't have an IP rating for water resistance (that I know of).
There is an extra wrinkle here though - the RCD spur you show is currently not listed in the Wiring Regulations as an acceptable way to add 'additional protection' in a bathroom, though there is conflicting information as to whether this was an error or deliberate.
Some people would say that means it can't be used on new installations to comply, but requires a more traditional RCD or RCBO protection
I still take the view that there are places where it is reasonable to use it, though adding more traditional RCD protection is a better option when it's available.
Is there any RCD protection in the property?
One final point - any work within the zones in a bathroom is notifiable under the Part P Building Regulations scheme, which generally means it has to be done by a registered person in the competent schemes.. There are other ways by notifying it yourself, but they can be costly...
Just checked from bathroom edge to wall 100 cm.Tha
Thanks for the advice . No RCD protection in the property. I also have the option of placing the RCD Spur outside the bathroom . I think from the edge of bath to wall is around 35 - 40 cm.
Although it would be OK more than 60cm from edge of bath, I'd personally put it outside where it's an option - that way you know all the wiring within the room has the protection - and also means it can be isolated/reset when necessary...Just checked from bathroom edge to wall 100 cm.
This is the view also taken by the NICEIC in their latest Connections magazine, published a few days ago. A 2 page article, ends with the conclusion that such RCDs do have a place, but should be noted on the certification as a departure.There is an extra wrinkle here though - the RCD spur you show is currently not listed in the Wiring Regulations as an acceptable way to add 'additional protection' in a bathroom, though there is conflicting information as to whether this was an error or deliberate.
Some people would say that means it can't be used on new installations to comply, but requires a more traditional RCD or RCBO protection
I still take the view that there are places where it is reasonable to use it, though adding more traditional RCD protection is a better option when it's available.
What is noted on the certificate as departure mean?This is the view also taken by the NICEIC in their latest Connections magazine, published a few days ago. A 2 page article, ends with the conclusion that such RCDs do have a place, but should be noted on the certification as a departure.
Thanks .All electrical work should be accompanied by a
All electrical work should be accompanied by a certificate. This can be a minor electrical works certificate, or an electrical installation certificate.
The purpose of these certificates is to declare that the work complies with the regulations.
As the current version of the regulations does not support the use of RCD fused connection units, if you choose to install one, then you must record it on the certificate as a departure from the regulations.
certificate. This can be a minor electrical works certificate, or an electrical installation certificate.
The purpose of these certificates is to declare that the work complies with the regulations.
As the current version of the regulations does not support the use of RCD fused connection units, if you choose to install one, then you must record it on the certificate as a departure
Thanks for pointing that out - I should probably read it a bit more often!This is the view also taken by the NICEIC in their latest Connections magazine, published a few days ago. A 2 page article, ends with the conclusion that such RCDs do have a place, but should be noted on the certification as a departure.
The RCD spur unit in question . Is there any requirements as to what amps the MCB at the consummer unit should be . Or does that depend on the amps of the RCD spur unit it self, weather its 10 amp or 30 amp. Does that make sense? Morning all.Thanks .
Hi . When powering a bath fan from the main circuit and no longer from the light circuit how do you stop powering from the lighting once the new cable from fcu has been put in place. The wiring from the rose to the junction box is 3 core and earth. So i gather do you cap the neutral.wire to stop the powering of the fan ? And will this still switch the fan on and off via the pull cord but no longer power the fan. Thanks.