D
Darkwood
My take on it---
The Swa should be earthed correctly at the supply end it does not need to be earthed at the load end as you have a separate earth core.
If the cable suffers damage to the outer sheath then corrosion to the SWA has less likely chance of isolating the steel from earth also if the is damaged in your spade scenario nearer the supply side as oppose to the load side and it was glanded only at the load then zs values may not meet as the fault has to travel nearly full length to the load end gland then back down the earth core effectively doubling the distance... you can take a zs at the unglanded end down to the armour to see if it complies or not.
All in all their really isn't an excuse for not earthing both ends of the swa as this would be good practice although earthing at one end is acceptable and pref' the supply end which will ensure zs is met. Their is no reason why a section of the ceiling board couldn't be removed and made good after IMHO this is just lazy attitude and loose excuses.
The Swa should be earthed correctly at the supply end it does not need to be earthed at the load end as you have a separate earth core.
If the cable suffers damage to the outer sheath then corrosion to the SWA has less likely chance of isolating the steel from earth also if the is damaged in your spade scenario nearer the supply side as oppose to the load side and it was glanded only at the load then zs values may not meet as the fault has to travel nearly full length to the load end gland then back down the earth core effectively doubling the distance... you can take a zs at the unglanded end down to the armour to see if it complies or not.
All in all their really isn't an excuse for not earthing both ends of the swa as this would be good practice although earthing at one end is acceptable and pref' the supply end which will ensure zs is met. Their is no reason why a section of the ceiling board couldn't be removed and made good after IMHO this is just lazy attitude and loose excuses.