There was just an open hole inside the steel box trunking and so allegedly nowhere to connect the gland and thus earth it, the option was to make a hole in the ceiling and gland onto the trunking that way but client forbid it , not right I know which is why I think it should be redone
well for a start...

regardless of what a client thinks...this should always come secondry to safety, conformance and common sense...
 
Looking it this I don't see how a sage disconnection would occur if the cable got damaged especially damage to the internal earth cable in the SWA.


think about it jamie

if a spade was driven through the cable shorting a line conductor to the armour or cpc ,

the OCD would operate under fault conditions if the zs was met .

If you inspected this install you would have concerns wouldn't you?

i would be wondering why the installer had entered from above and not glanded into the bottom of board . seems crackers to me .
 
I guess Jamie's point is that if the cable were partially cut through, you could leave the line and part of the armour intact but sever the CPC, hence losing the earth connection to the armour and the sub DB without the circuit protection operating. Normally if the CPC is earthed at the source, you can't cut through all of the armour without hitting the line, so the protection will operate before the last of the CPC is broken. It's a far fetched scenario but it's needless because it's a bodge.
 
Just gland both ends and make the installation safe. Its not that difficult. Do the job better than the regs advise, that way I can sleep at night.
 
I guess Jamie's point is that if the cable were partially cut through, you could leave the line and part of the armour intact but sever the CPC, hence losing the earth connection to the armour and the sub DB without the circuit protection operating. Normally if the CPC is earthed at the source, you can't cut through all of the armour without hitting the line, so the protection will operate before the last of the CPC is broken. It's a far fetched scenario but it's needless because it's a bodge.
And theres always the risk also of a meteorite strike as well
 
Heck, if you genuinely can't get an armoured gland on to anything, you could at least bodge it with an earth clamp (NOT suggesting this as good practice). Let's face it - you can't make it any worse.
 
Why didnt they gland into the trunking? Then have just the cores going into the board. Even terminating swa into a 1 gang mc box above ceiling then into trunking would be better
 
It shouldn't have been done like that, but there's no way you're going to get a spade through a 5 core 16mm2 SWA cable to the point where the earth core is cut, even if you've eaten your spinach.

Now, if you've got a mechanical digger or something then maybe, but it's pretty safe from spade strikes IMO.

Besides, the mcb would trip from the short circuit.
 
Other than the poor glanding this is being over complicated. How in the name of god are you going to damage a cable to the extent the CPC and the armourings are severed but the phases remain live?

Fit a feeder directional relay, should only cost a couple of grand + the pilot cable.

Crazy thread.
 
if the guy has got the SWA into the right hand CU through a hole, then there's no excuse for not fitting a gland.

Totally agree, even if the gland was hanging loose inside the containment area with a piranha nut or something and 16mm from there, just no excuse however you look at it. The only thing he seems to have got right is his choice of transport saving on fuel bills, he probably rides a horse.
 
Other than the poor glanding this is being over complicated. How in the name of god are you going to damage a cable to the extent the CPC and the armourings are severed but the phases remain live?

Fit a feeder directional relay, should only cost a couple of grand + the pilot cable.

Crazy thread.
with a spade apparently.

Is the OP available for trenching work next time we've got a long cable run to dig in? Could do with someone with that sort of force behind the spade on the job.
 