Discuss Is this installation safe or not? in the UK Electrical Forum area at ElectriciansForums.net
J
JamieK
Hi Guys
I am hoping to get some outside opinion on an installation that I don't think is safe but others do, I've drawn a shocking pic which I have attached to help describe the issue but I will try and detail it aswell.
This was a Solar PV installation in which the AC side was fed into the board on the left. The board is then fed underground using 16mm 4 core and earth SWA back to the main board in the customer building which is about 20m away under a bit of grass.
The SWA has a proper gland fitted where it enters the board on the left and has a 16mm supplementary bond connected to the MET inside the board. However, the left hand boards only connection to earth is through the SWA earth cable going underground to the main board MET 20m away.
The SWA feeding the main board is not glanded due to it coming through a ceiling in steel box trunking and the customer being adamant they did not want any damage in the newly decorated ceiling so the electrician just cut the SWA and terminated into the board without earthing the SWA with a gland - make sense!!??
The spark said that it is safe because the SWA is glanded at the left hand board side and a connection to earth is made through the internal 16mm earth in the SWA to the MET of the board on the right hand side.
My comment is that if (in the unlikely event) some form of excavation takes place and penetrates the soil above the SWA and the sand and the tape that was installed and causes damage to the SWA earth cable this will cause serious risk???
The spark says that is that happens the MCB will trip posing no risk to the person excavating but again my response is that this might not happen soon enough not to pose a danger.
Hope I have explained this as simply as possible I know its an odd one but any input very welcome indeed even if it is just to say I am wrong and it is safe.
Couple of questions
1 how deep is the SWA buried?
2 See no reason why the SWA can't be glanded
3 Is the supply at the left or right hand board?
both ends of the SWA need glanding. generally, if the armour is not uses as cpc, it only needs earthing at the supply end.
In effect what you are asking is: "Is it OK to earth SWA armour only at the destination, provided a copper core in the cable connects the destination to the source?"
I assume when you say MET in the left hand board, you mean the earth bar: The MET is at the origin. You have to start asking specific questions: What is the Zs and what protection is offered to the cable? What is the method of earthing and is the submain arrangement satisfactory as far as extending or exporting the equipotential zone is concerned? I don't think it is a plain yes or no kind of question.
It sounds like it could use some finesse, but if your concerns are that it won't meet disconnection times under a fault load then the only way of knowing is to do a Zs on the circuit and see if it complies with the upstream CPD as dictated by the BGB.
this is how i read it Lucien....
as you say there is now not only the length of the 16mm core to consider....but the length of the armourings as well when it comes to meeting a disconnection time...
better to earth the armourings at source..
if the guy has got the SWA into the right hand CU through a hole, then there's no excuse for not fitting a gland.
Thanks for the reply you are right that I should have stated the earth bar on the left hand side, I don't know what the zs is but the earthing arrangement was TNS. Looking it this I don't see how a sage disconnection would occur if the cable got damaged especially damage to the internal earth cable in the SWA. If you inspected this install you would have concerns wouldn't you?
get a Zs on the furthest point (this will be the armourings top end) to confirm....
There was just an open hole inside the steel box trunking and so allegedly nowhere to connect the gland and thus earth it, the option was to make a hole in the ceiling and gland onto the trunking that way but client forbid it , not right I know which is why I think it should be redone
well for a start...
regardless of what a client thinks...this should always come secondry to safety, conformance and common sense...
think about it jamie
if a spade was driven through the cable shorting a line conductor to the armour or cpc ,
the OCD would operate under fault conditions if the zs was met .
i would be wondering why the installer had entered from above and not glanded into the bottom of board . seems crackers to me .
I guess Jamie's point is that if the cable were partially cut through, you could leave the line and part of the armour intact but sever the CPC, hence losing the earth connection to the armour and the sub DB without the circuit protection operating. Normally if the CPC is earthed at the source, you can't cut through all of the armour without hitting the line, so the protection will operate before the last of the CPC is broken. It's a far fetched scenario but it's needless because it's a bodge.
Reply to Is this installation safe or not? in the UK Electrical Forum area at ElectriciansForums.net
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...