hi, just a quick question for installing a 32 amp hot tub a friend told me it HAS to be in SWA but I have seen lots of 32 amp tubs installed with 6mm twin and earth in conduit, Is he correct? and is there anything in regulations not allowing me to use twin and earth in conduit? many thanks
 
Without knowing the specifics of the installation it's hard to say. Is the cable run buried or clipped to a wall for example?
 
Twin and earth is not really designed for conduit . You would need large conduit for it too. Depending on the design E.G buried , I would go for SWA in ducting too.
 
hi, just a quick question for installing a 32 amp hot tub a friend told me it HAS to be in SWA but I have seen lots of 32 amp tubs installed with 6mm twin and earth in conduit, Is he correct? and is there anything in regulations not allowing me to use twin and earth in conduit? many thanks
As already stated the requirements depend upon the installation method, and it may be that SWA would be preferred, particularly if anything is buried. But in general there is no specific regulation requiring a particular wiring system for a hot tub and if a plastic conduit system provides adequate protection then it can be used.
As always when 'friends' or tradesmen make up their own regulations ask them to provide the regulation number they are referring to. It invariably silences them.
 

Reply to is twin and eath aloud in hot tub installs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi, looking for some advice, 6mm swa allready installed to a hot tub Client now wants additions and my calcs say the original swa is allready too...
Replies
26
Views
2K
Hi I posted recently about a hot tub supply I was needing advice with. One reply I got was directing me to a video by dave savery. Having...
Replies
9
Views
3K
Hi, having new hot tub installed, PME supply on 40A breaker 6mm twin clipped direct in loft down to 32A isolator, got some 10mm 2C laying around...
Replies
16
Views
2K
I would like to set up my hot tub wiring a few months before my tub arrives, I would also like to do it DYI. The run I'm panning is 100' from the...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock