Just gone self employed, Been asked to quote a job In a Small industrial unit ( 50ft by 48 ft)

Fuse board is in bottom right hand corner job is as follows

supply for burglar alarm at front of building ( Approx 18m Run in 20mm PVC conduit to Metal clad spur)

2 x metal clad twin socket approx 8m run from fuse board in 20mm pvc conduit With added rcd enclosure next to DB to protect sockets

2 x high level metal clad single sockets approx 10 metres and 34 metres away from DB in pvc conduit ( Same Circuit )

also in a unit next door a high level metal clad single socket in pvc 20mm conduit approx 8m from DB

Ive quoted £490 does this seem ok?

price also includes relevant tests and certification

Many thanks

Tom
 
Why not use RCBO for the sockets instead of enclosure? I would say that is ok price does that include materials?
 
Its a 3871 Mem 3 phase Db, Which doesn't take rcbos Unfortunately. Yes this price is for parts and labour :-)
 
Yeah i think that is a good price especially with materials i think i would have looked at it with the idea of how many days you think it would take and then add your materials on that like, but i think if you are happy with that price then thats what its about.
 
Im probably looking at 2 days after faffing about with the conduit. Materials came to around £210 , I added £140 day rate for each day to come up with the price. Whats your usual day rate up in brum?
 
well me i'm at £250 as after tax and overheads your not left with much! Businessman first in this game i'm afraid! But when i first started out i was at a similar rate to you, but having registration and insurance cost, van, tools etc you need to charge more to make it up!
 
The only overheads i have at the moment is the girlfriends need to shop!!, hopefully in a few years though ill have enough work to tackle overheads. Thanks for the help guys :-)
 
Without knowing the situation, use of building etc etc is PVC conduit the best method, with it being an industrial unit would SWA not be more suitable?


I was under the impression all socket outlets had to be Rcd protected?


No not at all...
 
Its being used for storage only ( conduit is high level and out the way) , Ah I Was told By an NIC-EIC representative while working for my old company that all socket outlets now require Rcd protection?
 
Aha so in what circumstances would I not need RCD protection? Places with no access from members of the public?
 
Its being used for storage only ( conduit is high level and out the way) , Ah I Was told By an NIC-EIC representative while working for my old company that all socket outlets now require Rcd protection?

ha thats funny, a while a go I saw some information given out by the NIC it was concerning RCD protection on sockets, it said domestic YES, Industrial NO and thats that. It depends on how its installed, its use and who is going to be using it.
 