I have two 40A swa cables from my main house consumer unit. This consumer unit serves the whole house and the two swa cables serve two consumer units in an extension. One is upstairs and has very little demand and one is downstairs with a higher demand.
I agree with DPG, you obviously have sufficient funds to contemplate a 3 Phase DNO install & employ an electrician, so without any further information on demand over 3 Consumer Units including the Main Unit I think you need professional help.
 
I have an Electrician ready to soon start the install before the 3 phase is connected. I am just trying to discover which solutions I can suggest & he can utilize. Sketching a several proposals will give the information of what is installed and what is required as a client.
I don't intend to do any work myself.
 
I have an Electrician ready to soon start the install before the 3 phase is connected. I am just trying to discover which solutions I can suggest & he can utilize. Sketching a several proposals will give the information of what is installed and what is required as a client.
I don't intend to do any work myself.

Leave the electrician to devise the best solution. Easy.
 
Thank you for all your replies and patience. I am probably a bit too inquisitive, possibly down to 50+ years as an engineer.

All the decisions will be made by the electrician and all of which I will respect.

The main query I still can't understand is the theory of using my two buried existing 3 core swa cables to supply the 3 phase from the new 3 phase meter to the new distribution board. One swa containing the 3 lives and the other containing the neutral. My understanding is although all the 3 live wires will be the same length and in the same direction, it is still not possible.

Which of the scenarios below prevent one swa for lives and the other for neutral, assuming the rating is within spec.

1. 3 phases only in swa, create unacceptable eddy currents and is never used.
2. 3 phases + neutral in swa, don't create unacceptable eddy currents.
3. 3 phases only in swa is ok but only if the load over all 3 is always balanced.
4. 3 phases only in swa will tolerate a small imbalance.
5. The neutral wire can't be used alone in swa.
6. The neutral wire needs to be encased with the lives to provide a current in the opposite direction to work.
7. The neutral wire needs to be the same length as the live wires.

Thanks in advance for any advice.
 
I think maybe the answer is based on how the SWA cables are correctly terminated into each Consumer Unit, I assume All metal C/U's. Also, what you are asking is a bit unconventional, to use the 2 existing SWA cables as 3phase you will need to be able to isolate together the main live conductors, which means line & neutral conductors. I would like to see how you achieve this. Makes nonsense of cable resistances too. Is there a way that you can rewire a circuit or circuits that are causing the high loads & connect to the less loaded C/ Unit?
 
1. 3 phases only in swa, create unacceptable eddy currents and is never used.
It is used for loads without a neutral (like your #3 case).

So if you had a delta-star transformer to generate your L1-3 & N arrangement in the far building it would be acceptable, but that would cost you far more than just putting in a new cable!

You do see separate L and N cables but they are normally alluminium armour to avoid the eddy current losses (and higher fault impedance which can limit disconnection times on over current protection alone).

If you can't get enough single-phase on the existing cable then faffing about with various ways to work around it are usually a wast of time as they are either not in keeping with one or more regulation, or they end up far more expensive than the simple and obvious approach.

If you do put new cable in then put it in some twinwall duct - or two. Then you can replace it later if you need to! Also it would allow you to put in a fibre network cable as well so you have as much bandwidth as you could ask for in the future.
 
It is used for loads without a neutral (like your #3 case).

So if you had a delta-star transformer to generate your L1-3 & N arrangement in the far building it would be acceptable, but that would cost you far more than just putting in a new cable!

You do see separate L and N cables but they are normally alluminium armour to avoid the eddy current losses (and higher fault impedance which can limit disconnection times on over current protection alone).

If you can't get enough single-phase on the existing cable then faffing about with various ways to work around it are usually a wast of time as they are either not in keeping with one or more regulation, or they end up far more expensive than the simple and obvious approach.

If you do put new cable in then put it in some twinwall duct - or two. Then you can replace it later if you need to! Also it would allow you to put in a fibre network cable as well so you have as much bandwidth as you could ask for in the future.
Thanks pc.

The 3 phase supply will now be directly from the grid.
It looks like each phase isolator will also have to isolate the neutral. I guess the neutral could be wired in series over the 3 isolators to isolate it by any switch? I expect that will be too simple.
 
It looks like each phase isolator will also have to isolate the neutral. I guess the neutral could be wired in series over the 3 isolators to isolate it by any switch? I expect that will be too simple.
Each single-phase DB coming off it will need its own independent DP isolator (i.e. the normal main switch).

However, you would be well-advised to have a 4P isolator off the meter(s) tails so you can safely do any work further down-stream without getting the DNO/billing company involved. This sort of thing:
 
Thanks pc.

The 3 phase supply will now be directly from the grid.
It looks like each phase isolator will also have to isolate the neutral. I guess the neutral could be wired in series over the 3 isolators to isolate it by any switch? I expect that will be too simple.

This is not a recommended solution.
 
Dno booked to install 3 phase.
Can two phases enter an existing 12way split consumer unit with 2 isolators and run some from one phase and some from the other?
Or will I need two consumer units.
 
I would ask your electrician now as he will be carrying out the work. You can spend a lot of time trying to make it work so why not just make a good job as the DNO will not connect if not happy with the install.
 
Yes, I have discussed various parts of the whole circuit. I'm interested to see if this is possible as it will save a lot of digging of trenches and can utilise the same cables. If I have to buy another cu for a different phase that's ok.

Your electrician would be better buying the equipment. Then he is responsible for. He will also probably not offer any warranty on items you have bought yourself.
 
I won't do anything until our meeting at the weekend. Can I assume from the responses that it is not possible to have two independent feeds into one split consumer unit. Or is it against regs.
 

Reply to joining two feeds into one consumer unit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
716
Hi everyone, a landlord is converting a house into two flats and wants a separate consumer unit for both flats upstairs and downstairs. He also...
Replies
13
Views
1K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
933
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
722
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock