Each single-phase DB coming off it will need its own independent DP isolator (i.e. the normal main switch).It looks like each phase isolator will also have to isolate the neutral. I guess the neutral could be wired in series over the 3 isolators to isolate it by any switch? I expect that will be too simple.
However, you would be well-advised to have a 4P isolator off the meter(s) tails so you can safely do any work further down-stream without getting the DNO/billing company involved. This sort of thing: