jutty

in my house the c/u is in the garage so i have changed that and added a ring with 4 sockets in the garage, new lighting circuit boiler supply and outside wall lights either side of garage door!!

my question is the existing circuits in the house ie. old ring and old house lights etc, i only have to earth loop test these dont i???? is this correct???

obviously the garage circuits i have done is a full test!

this is my major job for the inspection, should the outside wall lights be on the RCD side or doesn't it matter? this was carried out before the 17th edition too

any help appreciated thanks justin
 
Nope you need to do full testing & test all the old circuits as you have changed the cu.
It'll be an instant fail if you dont.

No the lights dont need to be on the rcd if it was designed & installed pre July 1st.
 
Last edited by a moderator:
Well as its for an assessment I'd be inclined to make sure it's right upto scratch.

But if you change a cu you as the installer are then responcible for every circuit served by that cu, and as such have to ensure it is up to current regulation requirements.
Thats why most sparks do a pir before changing a cu.
 
ok will make sure it is top notch then!

thanks for the advice

a quick question regarding my test, there are some sockets i can't get too, 1 behind a radiator!!! 2 in the kitchen that have been tiled and grouted around!!
so can i write on the cert. that unable to inspect some sockets in the existing installation details? along with green sleeving used not green and yellow...im sure its ok to write the things that i have found that are not correct on the cert as a recommendation to the customer!
will this cover me and will the NICEIC inspector be ok with that?

thanks
 
Last edited by a moderator:
there are some sockets i can't get too, 1 behind a radiator!!! 2 in the kitchen that have been tiled and grouted around!!
so can i write on the cert. that unable to inspect some sockets in the existing installation details?
thanks

Yes where it says details of existing installation, just make a note along the lines of "unable to complete testing at XXXsockets due to *****"
& as a comment in deviation section make a note of wrong cpc sleeving used.
 
Easyfox,

WHAT IF CUSTOMER DOSENT WANT A PIR BEFORE CHANGE OF CU DO YOU JUST WALK AWAY OR DO YOU TAKE THE CHANCE
 
Easyfox,

WHAT IF CUSTOMER DOSENT WANT A PIR BEFORE CHANGE OF CU DO YOU JUST WALK AWAY OR DO YOU TAKE THE CHANCE

When I say PIR I dont mean a full on job.
It normally goes as follows.

Call from customer asking for a cu change, I give them a time/date to visit to price job up.
Turn up with Fluke & screw drivers in hand run through a few wants that they want (give my ideas to make my life easier during install), tell them that I'll just need to turn cu off to do a few tests free of charge (add the cost to the cu change quote), do quick cont test/IR across whole board/Ze/pfc/pscc. quick check of equip bonds (dont bother with supplimentary bonding now) & thats it.
 

Reply to just booked my NICEIC part p inspection in the Business Related area at ElectriciansForums.net

Similar Threads

Hi I have a Corby 7700 trouser press it is a 220w model, 3 years 10 month old. On Friday it stopped working, so I took it to the garage ready...
Replies
1
Views
615
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
405
Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
309
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
781
Hi all, I am going to fully rewire my house. What do I HAVE to do once I’ve rewired it? I am an approved spark, but do not have part P. Do I need...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock